How you take care of a motor from over loading and what are
the different overloading ratings of different motors?
Answers were Sorted based on User's Feedback
Answer / daher
use overload circuit breaker to protect it, thermal
overload protects your motor againts overloading or/and
overthermal switch mount it on the motor stator.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / aditya sharma
Overload relay will be use for overload protection
Different different rating of overload relay
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nikhan
# 1 Motor
Rating Motor F.L.C in Amp
0.25 KW 0.4725
0.37 0.6475
0.5 0.9625
0.75 1.3125
1.1 1.925
1.5 2.625
2.2 3.85
3 5.25
3.7 6.475
4 7
5 - 5.5 9.625
7.5 13.125
9.3 16.275
11 19.25
15 26.25
18.5 32.375
22 38.5
30 52.5
37 64.75
45 78.75
55 96.25
75 131.25
90 157.5
110 192.5
132 231
150 262.5
160 280
200 350
250 437
Is This Answer Correct ? | 0 Yes | 2 No |
Motor
Rating Motor F.L.C in Amp
0.25 KW 0.4725
0.37 0.6475
0.5 0.9625
0.75 1.3125
1.1 1.925
1.5 2.625
2.2 3.85
3 5.25
3.7 6.475
4 7
5 - 5.5 9.625
7.5 13.125
9.3 16.275
11 19.25
15 26.25
18.5 32.375
22 38.5
30 52.5
37 64.75
45 78.75
55 96.25
75 131.25
90 157.5
110 192.5
132 231
150 262.5
160 280
200 350
250 437.5
Is This Answer Correct ? | 1 Yes | 5 No |
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
three phase 180kva diesel generator can take how much load in amp and what is formula to get this?
Which type of alternator used in power station?
why does connected a indutor with mnsformeretering core of current transformer ?
How to select power cable for machine
Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?
is it necessary to earth the rmu before cutting off the transformer winding?if yes why?
from 33kv to 440v 2mva transformer how much full load current will be at ht side and lt side and which range of ctpt will be used?
How can we design a HVAC Plant room which includes AHU,FCU,Chillers,Cooling towers, Pumps etc & how will they work? any Drawing if possible?
If Neutral Grounding Resistor (GR) failed/shorted. Is it repairable.
when we increased the current what do ?