Answer / vinod singh

current coil is connected in series so that its resistance
should be as minimum as possible otherwise there will be
voltage drop and power loss during normal working condition.

Is This Answer Correct ?    53 Yes 6 No

why current coil has less number of turns compared to pressure coil?..

Answer / anindita

current coil is connected in series with the load whereas
pressure coil is connected parallel to the supply, that is
pressure coil is connected across the voltage source.
current coil have lesser number of turns than the pressure
coil so that the impedance of the pressure coil increases
and it draws minimum current from the circuit,causing lesser
error in the reading.

Is This Answer Correct ?    22 Yes 6 No

why current coil has less number of turns compared to pressure coil?..

Answer / kundanmalani1990

bcz the CT are connected to the series in supply line so
that high current pass through the line and high current to
absorbers to CT so current coil has less number of turns
compared to pressure coil !!!!

Is This Answer Correct ?    12 Yes 11 No

why current coil has less number of turns compared to pressure coil?..

Answer / ansuman

current coil have to measure current ; to achieve it less resistance is given by providing less number of turns in current coil.

Is This Answer Correct ?    3 Yes 2 No

why current coil has less number of turns compared to pressure coil?..

Answer / raju kumar

this is because,current supplied to the load may be more and more and wattmeter may get current reading of power supplied

Is This Answer Correct ?    2 Yes 3 No

why current coil has less number of turns compared to pressure coil?..

Answer / raj kumar

Current coil connected in series with the load.in series circuit current is same and voltage different.if we are increasing the number of turns in the current coil as like pressure coil number of turns.
First load current only passes through the current coil because series circuit.so current increases automatically voltage drop will increase.so error will occur.it will not show the correct reading.

Is This Answer Correct ?    1 Yes 2 No

why current coil has less number of turns compared to pressure coil?..

Answer / nithi

IF CURRENT COIL IS PROVIDED WITH MORE NO. OF TURNS,THEN IT
WILL DROP MORE VOLTAGE ,AS IT IS CONNECTED IN SERIES WITH
THE LOAD.

Is This Answer Correct ?    7 Yes 9 No

why current coil has less number of turns compared to pressure coil?..

Answer / mr. utsav jain

bcz current coil connected in series and the pressure of the current coil is very high so it will produce large voltage drops.
in parallel condition obtain the high voltage large no of turns.

Is This Answer Correct ?    2 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

what is the different between second harmonics and third harmonics ?

1 Answers  


control wiring purpose,standards, ferrule code standard, interlock, schematic, symbol

1 Answers  


I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula

1 Answers   Wipro,


what is difference between low voltage and high voltage

3 Answers  


what are the condition that makes hooter blow?

0 Answers  






sir, in a industry present pf is 0.54 pf 25hp power is there its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.

2 Answers  


what's producer of XLPE cable laying in undergroung

0 Answers  


we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.

0 Answers   MTN,


What is IDMT? What is the principle

3 Answers  


How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5

1 Answers   L&T,


what is difference between inductive and reactiveload?

5 Answers   ONGC,


i heard that power factor(PF) is the main concern for industries, if they are maintaining PF around 0.6 they will be fined for that. now the question is, how can they improve the PF ranging between 0.9 to 0.95 which is safe for them i,e escaping from the fine?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)