why current coil has less number of turns compared to
pressure coil?
Answers were Sorted based on User's Feedback
Answer / vinod singh
current coil is connected in series so that its resistance
should be as minimum as possible otherwise there will be
voltage drop and power loss during normal working condition.
| Is This Answer Correct ? | 53 Yes | 6 No |
Answer / anindita
current coil is connected in series with the load whereas
pressure coil is connected parallel to the supply, that is
pressure coil is connected across the voltage source.
current coil have lesser number of turns than the pressure
coil so that the impedance of the pressure coil increases
and it draws minimum current from the circuit,causing lesser
error in the reading.
| Is This Answer Correct ? | 22 Yes | 6 No |
Answer / kundanmalani1990
bcz the CT are connected to the series in supply line so
that high current pass through the line and high current to
absorbers to CT so current coil has less number of turns
compared to pressure coil !!!!
| Is This Answer Correct ? | 12 Yes | 11 No |
Answer / ansuman
current coil have to measure current ; to achieve it less resistance is given by providing less number of turns in current coil.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / raju kumar
this is because,current supplied to the load may be more and more and wattmeter may get current reading of power supplied
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / raj kumar
Current coil connected in series with the load.in series circuit current is same and voltage different.if we are increasing the number of turns in the current coil as like pressure coil number of turns.
First load current only passes through the current coil because series circuit.so current increases automatically voltage drop will increase.so error will occur.it will not show the correct reading.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / nithi
IF CURRENT COIL IS PROVIDED WITH MORE NO. OF TURNS,THEN IT
WILL DROP MORE VOLTAGE ,AS IT IS CONNECTED IN SERIES WITH
THE LOAD.
| Is This Answer Correct ? | 7 Yes | 9 No |
Answer / mr. utsav jain
bcz current coil connected in series and the pressure of the current coil is very high so it will produce large voltage drops.
in parallel condition obtain the high voltage large no of turns.
| Is This Answer Correct ? | 2 Yes | 4 No |
I If i have 2kv ups in which 38Amp *8battries hou many hour's back up i get from 600Watts
HOW DO I CALCULATE OVER LOAD RELAY & CONTACTOR IN DOL STARTER? & in dol why it is require circuit breaker?
what is the meaning of osr in transformer.
Explain Power factor in simple words
maximum transmission voltage in india ? & where is it situated ?
What is meant by Guard relay ?
what is AVR in alternator how its work?
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?
Difference between shunt, PMG and AREP excitation. Which is the most reliable between PMG and AREP.
what are the materials used in HRC fuse
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)