While starting a high capacity motor, it takes 6 times the
full load current. Why it doesn't trip relay or CB's in
that network?
Answers were Sorted based on User's Feedback
Answer / a.alexander
Motor Current will take 6 to 7 times for Just 3 to 6 Sec
only. and Cb was with stand the Current in Same Seconds
.That is Set point of CB full load Current.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / blake_australia
The starting current for an induction motor is around 6x
full load current, however this is only for ~3cycles. Which
is about 0.06seconds (for 50Hz power).
Circuit breakers chosen for motors (D curve in Australia)
delay for more than this 0.06seconds. The curves can be
seen in any NHP breaker selection catalog. Protection
curves are more indepth than this, reading into these will
help.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / praful nandankar
Circuit breakers are given sufficient delay time,hence the
relay will not trip when motor takes 6 times the full load
current.
praful nandankar
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sunthosh080
usually when you see the relay technical details there will
CLASS type (5-30)
When your motor is taking 6 times for 5 sec you have to
select 5. So that your relay doesnt trip during this and it
depends on the application also.
If it fan application , then it would be around 15-20.
If the relay is tripping during motor starting then it
CLASS problem.
| Is This Answer Correct ? | 0 Yes | 4 No |
What is the Designing & Selection Procedure for a DG/Transormer of rated capacity?
How multimeter shows phase to phase voltage 440V & phase to neutral 220V.
can a motor acts as a generator
How can determine cable size with respect to cable length and area in mm2
Which is is best option for 33 kv line incomer.I am Desinging the panel for new projects and i would like to get Your opinion on this Vcb or sf6. Please help me with your replies. Thanks D p singh
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??
what is relay multiplier
1 Answers Atomic Energy Commission, Bhel, Wipro,
at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)
0 Answers Ebrahim Textile, Siemens,
Why does inductor is connected to dc supply? or what is the role of an inductor when connected to DC source?
In synchronous generators field is rotor and armature is stator.Can we take the output at the rotor in case of synchronous generator by the dc excitation on the stator?
why Line voltage =1.732XPhase voltage what mean by 1.732
I want to know that a 160kva diesel generator contains capacity of 160kva on each phase like R=160 Y=160 B=160 total RYB=480kva or it is total capacity of all there phases like RYB=160kva ... thanks in advance ...
2 Answers jlpl, JP Saraswat Engineers,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)