While starting a high capacity motor, it takes 6 times the
full load current. Why it doesn't trip relay or CB's in
that network?
Answers were Sorted based on User's Feedback
Answer / a.alexander
Motor Current will take 6 to 7 times for Just 3 to 6 Sec
only. and Cb was with stand the Current in Same Seconds
.That is Set point of CB full load Current.
Is This Answer Correct ? | 12 Yes | 4 No |
Answer / blake_australia
The starting current for an induction motor is around 6x
full load current, however this is only for ~3cycles. Which
is about 0.06seconds (for 50Hz power).
Circuit breakers chosen for motors (D curve in Australia)
delay for more than this 0.06seconds. The curves can be
seen in any NHP breaker selection catalog. Protection
curves are more indepth than this, reading into these will
help.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / praful nandankar
Circuit breakers are given sufficient delay time,hence the
relay will not trip when motor takes 6 times the full load
current.
praful nandankar
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sunthosh080
usually when you see the relay technical details there will
CLASS type (5-30)
When your motor is taking 6 times for 5 sec you have to
select 5. So that your relay doesnt trip during this and it
depends on the application also.
If it fan application , then it would be around 15-20.
If the relay is tripping during motor starting then it
CLASS problem.
Is This Answer Correct ? | 0 Yes | 4 No |
How is a capacitor bank is designed ?
Is there thumb rule to calculate how many Insulators to be used for Transmission line of different volatges
how the transmission voltage ranges are decided like 11kV,33kV,66kV,132kV,220kV,400kV,725kV.... why not choose the transmission line voltage as 23kV,164kV,440kV?? what's the reason??
What is clean Earth System ?
Explain the different regions in frequency response?
define briefly the function of an ac electric generator (alternator)?
How frequency meter measuring frequency? What is the principle of frequency meter?
what is the operating time for LBB and how does the LBB relay realise whether cb is opened or not?
For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?
What is Anemometer used to measure?
why we are using auto transformer in sub station mostly???
What happens if the series current double?