what is derated current of power cable & what is formule to
find derated current?
Answer / mahesh sali
See , the formula for derated current is nothing bu derated
factor .
Mostly derated factor depends upon the following points.
Way of cable laying i.e. on cable trays / duct / pipe etc(
open to air or into the Hume pipe or under ground )
Cable laying by grouping & having distance between two
cable as per individual manufacturer recommandation .
Each manufacture gives the deration factor for the above
stated point.
Deration means your cable carry the less current below your
rated capacity due the above reason.
take example.
suppose
1.5 sq.mm. cu carrying the current around 12 amp.in open to
air at 25 deg.c ref. temp. as per cable manufacturer
after considering the above stated point
if suppose my deration factor would be around 0.6
then deration current of above cable would be - 12 *
0.6=7.2amp
it means that your cable carry the less cuurent do the way
of laying , temp. cable grouping etc.
i hope above inf. sufficient for understanding
thanks
Is This Answer Correct ? | 11 Yes | 3 No |
what is DG A,B,C,D check?
lenz law application and define
SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS
can u describe the method used for protection of transmission line.
Why grounding is generally done in supply end?
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?
Let's say I have 2 current carrying conductors C1 and C2 carrying currents of 5A and 10A. They are brought close to each other from a distance of infinity to a distance of 10cm away from each other - 1. What would be the values of current flowing in each conductor when (taking into account effects of interference of each conductor on the other) - a. The currents are AC b. The currents are DC c. C1 is AC and C2 is DC Please explain your answer with mathematical equations and formulas. Please specify the final numeric answer. Please make assumptions and clearly specify them.
What is Autodialer used in FAS????
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
0 Answers ABC, Reliance Life Sciences, TCS,
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
How to test REF relay testing for LV panel as per Kahramaa standard?
i have faced a problem in ro plant grunfos make bm30type pump it is 22kw pump. We start this pump using siemens 3rw 4423-ibc44, 30kw softstarter but this soft starter will frequently failier so we planed to change dol starter. So pls tell anybudy its possible or not.