Answer / m l sharma
When we calculate the cable size by Amp then we consider the type of load (inductive,resistive, capacitive)& voltage drop.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ayman
by knowing the load current and voltage and the length
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pk
It depends on the length from source to load, maximum permissible loss and thermal capacity of insulation.
Resistance = Rho x Length / Cross Sectional Area
Voltage Drop = Current in the wire x Resistance
The resistance of the wire leads to voltage drop
Depending on how much voltage drop is permissible at the load the area should be chosen appropriately
The second factor is heat produced.
Energy Loss = heat produced = I^2 x R.
This will lead to a temperature increase. The insulation should be able to handle this rise. Also the losses should be as low as possible to improve efficiency.
This is the theory. Thumb rules of 3-5 Amperes per sqmm are prevalent in the industry
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravinder paul
what is the size of 7/14,7/16,37/16 cables in mm
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / farhat ali
cable length is 6 Meters load is 152 Amp. 3 phase 110 v.
what size cable is used for that
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / suthan prabhu
for copper cable 1Sqmm can carry 1.92 Amps .
| Is This Answer Correct ? | 18 Yes | 32 No |
Hi friends. is it possible that SCADA System through RTUs can connect Via PLCC Communication carriers ? thanks
How many size of cable required for a 300m long and 30kw inductive lode
what are different type of triping equipmen like MCB,MCCB and their differences
3 Answers ABB, Schneider, UPPCL,
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
What is the difference between Static and servo controlled voltage stablizer?
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
what ll happen to current if two phases get short circuited
Difference between field rheostat and armature rheostat.
how to protect transformer
What is the make of breakers, transformers, generators? What are their capacities and ratings?
A resistor,inductor and capacitor are connected in series respectively.Voltage across resistor is 40v,across inductor is 70v,across capacitor is 100v.Then what is the total voltage applied across the elements?
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)