i have 2 motor of same rating. on no load condition one
motor take 1.6A but other motor is taking 4.8A. what is the
reason of this. please explain with proof.
Answers were Sorted based on User's Feedback
Answer / b.b. singh
one motor has connected in star then it taking 1.6A &
another is connected in delta so it taking 4.8A.
| Is This Answer Correct ? | 16 Yes | 1 No |
In case of 3 phase motors,
the motor takes higher current might have incorrect winding ratio which may cause unbalancing of 3 phase current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ashok sharma
OK. It is right that in star motor taking 1.6A & in delta
motor is taking 4.8A. but Please prove this with example.
Suppose both motors are new .
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / sivakumar
FIST U WILL CHEK THE HP RATHIG THEN NEXT CHEKED AMPS
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / loboreliance2003
The motor drawing 1.6A on no load appears to be okay.The
motor drawing 4.8A on no load appears to have a fault. the
winding may be having not proper megger value. Or even
rewinding of this motor may have been done improperly. You
will not find this condition in new motors from original
manufacturer.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sakthivel
first you are check the bearing and terminal board and all
so check starter conduct knob and verify the electrical
parameter and all check pump and so impellerside
| Is This Answer Correct ? | 0 Yes | 3 No |
What is the instrument to check the rotating diode fuse of alternator in running conditions?
How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?
i want to trigger ATS (Mains +Generator )from external system could any body help me in this regard ?? is it posible if yes please tell me how?
is it possible to run the any motor when winding grounded? how?
how to calculate the current carrying capacity of a 25 & 16 kva distribution transformer.
What is the difference between ground and neutral ?
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
Metal covered multiconductor cables shall employ a marker tape located within the cable running for its complete length in lieu of cable surface marking. Is it true or false?
What is the types of HT motor testing
HOW DG WORKS ?
What is the need of motor starter?
Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)