i have 2 motor of same rating. on no load condition one
motor take 1.6A but other motor is taking 4.8A. what is the
reason of this. please explain with proof.
Answers were Sorted based on User's Feedback
Answer / b.b. singh
one motor has connected in star then it taking 1.6A &
another is connected in delta so it taking 4.8A.
| Is This Answer Correct ? | 16 Yes | 1 No |
In case of 3 phase motors,
the motor takes higher current might have incorrect winding ratio which may cause unbalancing of 3 phase current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ashok sharma
OK. It is right that in star motor taking 1.6A & in delta
motor is taking 4.8A. but Please prove this with example.
Suppose both motors are new .
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / sivakumar
FIST U WILL CHEK THE HP RATHIG THEN NEXT CHEKED AMPS
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / loboreliance2003
The motor drawing 1.6A on no load appears to be okay.The
motor drawing 4.8A on no load appears to have a fault. the
winding may be having not proper megger value. Or even
rewinding of this motor may have been done improperly. You
will not find this condition in new motors from original
manufacturer.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sakthivel
first you are check the bearing and terminal board and all
so check starter conduct knob and verify the electrical
parameter and all check pump and so impellerside
| Is This Answer Correct ? | 0 Yes | 3 No |
16kv transformeris stolen in my village.and department is not taking action.then what should i do.any shortcut .please help any idea
1.Difference between vcb and Acb and partes. 2.Difference between STS and ATS.
In a 3 phase 4-wire system. For a 3.5 core cable if all loads are single phase and balanced, what will be neutral current? will it be sum of all phase currents? Or it will be zero? And if loads are unbalanced what will be neutral current?
Why diesel tank kept in 990 ltrs
what is the difference between current voltage transformer and current transformer and where it is used?
We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv is applied in its primary what will happen?
why we are using KVA rating for transformer,not KWh rating?
what is IMPEDENCE? FORMULE?
arrange to send solved question and answer its easy to study and understand the thing, because of Exam is to be conducted shortly
Comment on the working principle of operation of a single-phase transformer.
Can we use the Poly Phenly Sulphide instead of Poly Phenly Ether? Do clarify your opinion.
hai now i am working as a electrical design engineer in construction field can i get a job in oil and gass field or power plant project as a electrical design engineer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)