Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to callibrate a new i/p converter

Answers were Sorted based on User's Feedback



how to callibrate a new i/p converter..

Answer / binu

Connect the input air suply of around 5 to 7 Barg. Feed 4
mA through the calibrator, the output aire pressure gauge
shal indicate 3 psi. Feed 20mA through the calibrator, the
output air pressure gauge shall indicate 15 psi.

Is This Answer Correct ?    25 Yes 4 No

how to callibrate a new i/p converter..

Answer / guest

hi sanjay
1. AIR SUPPLY
I/P input - 1.4kg/cm2
Out put - 0.2 to 1kg/cm2 ok

2.input signal= 4-20 mA

i.connect the air supply to input with the hepl of REGULATOR i.e 1.4kg/cm2
ii.connect the MASTER GAUGE to OUT PUT ok

Apply the signal

i. 4mA- 0 kg/cm2 (if not Zero/0.2kg/cm2 Adjust Zero adjustment Screw)
ii. 20mA-1 kg/Cm2 (if not 1kg/cm2 Adjust Span adjustment Screw) ok.

then 8, 12, 16mA.
min. and max. is ok the remaining will perfect automatically i.e 8,12,16mA.

and MAIN IMP POINT is ON the I/P's Ckt board Side 4 adjust ment buttons is there and adjust that buttons Direct and Revese Actions ok

Is This Answer Correct ?    20 Yes 0 No

how to callibrate a new i/p converter..

Answer / asif javaid

FIRST SEE ITS PRESSURE RANGE APPLY INPUT PRESSUR 5PSI
MORE THEN MAXIMUM RANGE OF OUTPUT PRESSURE AND SEE ITS OUT
PUT THEN APPLY 4MA AND SEE OUTPUT SIGNAL 3 PSI NOW ADJUST
3 PSI FROM ZERO ADJUSTMENT SCREW NOW 8 12 16 &
20MAAPLY AND CHECK MAX PRESSURE RANGE NOW ADJUST FROM SPAN
SCREW

( RANGE CAN BE DIFFERENT FROM 3 TO 15 PSI )

Is This Answer Correct ?    7 Yes 0 No

how to callibrate a new i/p converter..

Answer / haridass

Friends, plz understand the question first. The
interviewers has mentioned "how to calibrate a NEW i/p
converter?"
Why the new i/p needs calibration?

Your answer must be like this..

"Sir, the new i/p would be factory calibrated with high
accuracy master instruments, so before we commission it in
the plant we have can check its output by applying proper
signal, unless we have good accuracy masters we no need to
disturb the calibration. If yes, we can do the calibration
using the 30psi regulated supply, 4-20 mA source, and
receiver gauge."

Is This Answer Correct ?    8 Yes 1 No

how to callibrate a new i/p converter..

Answer / charlie daubitz

There can be a jumpper on the I-p converter to set the
range. There are more accepted ranges than only 3-15 psi.

Is This Answer Correct ?    4 Yes 0 No

how to callibrate a new i/p converter..

Answer / binu

Dear Sanjay,

Hope you are adjusting 4mA with "Zero" screw and 20mA
with "Span/range" screw. I feel that you might have
adjusted the 3 psi with range screw.

Is This Answer Correct ?    0 Yes 2 No

how to callibrate a new i/p converter..

Answer / sanjaymaven

i follow your above procedure
i use 0-30 psi pressure gauge
when i feed 4 mA gauge show 3 psi, gradually i increase mA
, simontaneously pressure increase.At 10 mA gauge shows maxm
20 psi. i little adjust the range screw but nochange on
gauge. now what will i do .please sujest

Is This Answer Correct ?    3 Yes 9 No

Post New Answer

More Instrumentation Interview Questions

What is the main three inputs of DCS?

1 Answers  


Yokogawa dcs nodes advantages?

0 Answers   Petrochemicals,


how pressure transmitter work, what is its principal to measure and how its generate signal. for pressure transmitterinstallation which precautions must be taken ??

0 Answers  


where uses EXe /EXd/Exo/Exn/Exp/Exq/EXia

0 Answers  


what is "smart" in smart transmitter ?

4 Answers  


what is the input of conductivity sensor and meter during the calibration time and what is the output?

2 Answers  


Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .

2 Answers   Jindal, Sadara Chemicals,


one rtd sensor which is connected at middle of distillation column where actual temp. is 100deg but when we tight this sensor at thermowell end it goes down to 90 deg & when remove from the thermowell(but sensor end dipped in well) showing actual reading, what is reason?

3 Answers  


For crude application in floating roof tank, how to calibrate a DP Transmitter? How is the floating roof weight considered?

0 Answers  


what is the dp across a orifice plate & how much is permanent pressure across an orifice plate.

2 Answers   HPCL,


NPN transistor, SCR, Zener diode, LED, Varactor diode, Vortex meter, RTD, Resistor, Crystal

0 Answers   CCIE, RTD,


What is difference b/w absolute & gauge pressure? EXPLAIN

2 Answers   IFFCO,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)