Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why we do 2 types of earthing on tranformer ie:body earthing
& nutral earthing , what is function.
i am going to instal a 5oo kva tranformer & 380 kva DG set
what should the earthing value

Answers were Sorted based on User's Feedback



why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / jayesh patel

Body earthing is used for body leakage current to earth &
not humen body harmful. Neutral earthing is used for
unbalance current pass through neutral & its goes to earth
& not effect on other phases voltages/load.

Is This Answer Correct ?    82 Yes 4 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / guest

The two types of earthing are Familiar as Equipment
earthing and Sysytem earthing.
In Equipment earthing: body ( non conducting part)of the
eqipment shold be earthed to safegaurd the human beings.

system Earthing : In this neutral of the supply source (
Transformer or Generator) should be grounded. With this,in
case of unbalanced loading neutral will not be shifted.so
that unbalanced voltages will not arise. We can protect the
equipment also. With size of the equipment( transformer or
alternator)and selection of relying system earthing will be
further classified into directly earthed,Impedance
earthing, resistive (NGRs) earthing

Both are equally importantand compulsory. As per your
requirement Earth pit value will be below 10 Ohms.

Is This Answer Correct ?    53 Yes 3 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / sarav

Ans 3 is mostly correct. But the value of the earthing is
below 2 Ohms.

Is This Answer Correct ?    19 Yes 2 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / riyadh

Star connection T/f's mid point of b/w two phase should be
neutral point . tat point is to be earthed ,
Body earth goes to ground the leakges in the T/f's to
protect human beings frm harmful

Is This Answer Correct ?    27 Yes 15 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / sidhu

value shud be below 1 ohm

Is This Answer Correct ?    14 Yes 7 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / kunwar singh

Body Earthing : To ground any leakage current flowing in the e body of transformer & to protect human Body.

Neutral Earthing: To ground the unbalanced current in neutral.

The earth resistance should be below than 2 ohms.

Is This Answer Correct ?    7 Yes 3 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / nitin naik

1)Body Earting:- It is a part of earthing process were we
are connecting the metallic part of the equipment to the
general mass of the earth (earth is a zero potential) to
ensure any leakage current due to failure of the insulation
of the active conductor. If it is not ensured & suppose
there is leakage current it may cause electrical shock to
the person touching the metallic part of the equipment.
2) Neutral Earting:- It is being ensured & essential where
we are installing distribution transformer (Delta to star)
& Three phase neutral DG set, Neutral earting is the
process of earthing the star point of the secondary winding
of transformer & star point of the alternator winding to
the general mass of the earth. It is essential to eliminate
the return current in neutral due to unbalanced voltage &
further to eliminate unbalance potential between the
circuits.
Note:- In both the case earth setups resistance should
below 2 Ohms.

Is This Answer Correct ?    5 Yes 1 No

why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is functi..

Answer / pramod sharna

Basically earthing neutral earthing its protects fluctuation
of current and overloading and safety of equipment.

Body earthing is used to leakage of current.

Is This Answer Correct ?    3 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

why are you use the crgo core lamination in transformer

6 Answers  


An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm

0 Answers  


What is Magnetic Current Test of Transformer.

2 Answers  


what is static switch where it can be use?

1 Answers  


what is Aircraft earthing and what does it do?

6 Answers  


How to do bus bar short circuit calculation for 230KV/11kv, 60 MVA Substation?

0 Answers   ABB,


when the Transmission and Distribution network where is the "feeder" lines are located? and why should be used in T&D network.....

0 Answers  


what is surge impedance loading and it's significant in power system?

2 Answers  


What is the exact load current needed for a place which has 100nos of bulb of each 100w?

2 Answers  


what is invertor supply and raw powersupply

0 Answers  


( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq

2 Answers  


Is there any specialised book to refer about fault level calculation both in MV and LV side??

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)