how to calculate the capacitor rating for improving power
factor
Answers were Sorted based on User's Feedback
Answer / r n seth
capacitor required is too be calculated from required power
factor to desired power factor.the formula is-
Req. Cap in KVAr= Tr. MVA* PF( tan cos-1(existinf PF- tan
cos-1(desired PF))
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / engr. tariq
Formula :
C = P (tan|old - tan| new) divided by Omega (w) and then
divided by Voltage (RMS) or Vrms.
theta (|) can be calculated by knowing cos theta OR power
factor. Example PF is 0.77 then Cos theta = 0.77 and Cos
inverse (0.77) = 39.646 = Theta OLD. Now
Now if i want to improve PF to 0.9 then theta = Cos inverse
0.99 = 25.841 = theta New.
After calculating theta put it in the Given formula to
calculate Capacitance required.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / engbri
Another way i use is to take the PF and turn it into an
angular measurement in degrees. using j notation and the
magnitude of the wave you can calculate the size of
resistance, or real component and the size of the inductive
reactance or the -J component. Do this with a simple Polar
to rectangular conversion, if you cant your calculator
probably can. Then making the capacitive reactance equal to
the inductive reactance cancels it as they are oposites.
Then using the formula Xc = 1/2piFc transpose for c which
gives c =1/2piFXc. however as the cpacitor is taken as
ideal and with no resistive component this will never
reduce the PF to zero.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / charu gupta
kVAr Rating = kW(tan A - tan B)
Where kVAr rating is the size of the capacitor needed,kW is
the average power drawn, tan A is the trigonometric ratio
for the present power facotr, and tan B is the
trigonometric ratio for the desired PF
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / engr. tariq
Please note that in answer # 5 omega (w) is equal to the
frequency of the system.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / salman
to find above answer so we can directly go through
contract technical book this easiest way.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / pavan vyas
as a thumb rule it should be 1/3 of load kw & theoretically
we can select from the chart
| Is This Answer Correct ? | 8 Yes | 13 No |
please send the IS strandard for electrical to sakthi_murugan86@yahoo.co.in
what is the difference between earthed and unearthed cable?
24 Answers Cords Cable, Essar, Torrent Power,
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
Difference between hopkinson and swinburne's test
what are the dimensions for 200 kva transformer plinth (plateform),in which pcc m20 is used..
If Neutral Grounding Resistor (GR) failed/shorted. Is it repairable.
what will happen if ac motor given dc supply?
what is meant by negative conductor?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
Why should we use Star-Delta connection in step down power transformers?
what is the difference between general inverter and solor inverter clerly explain plz
what is the maximum load in MDB,SMDB and DB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)