What power factor maintain you maintain at u r organisation

Answers were Sorted based on User's Feedback



What power factor maintain you maintain at u r organisation..

Answer / ajit singh

yes the power factor in any organization should maintain from .8 to .99 or 1,

Is This Answer Correct ?    13 Yes 3 No

What power factor maintain you maintain at u r organisation..

Answer / laxminarayan

In Industrial sector there are more inductive loads.The
inductive loads draws more load current.So maximum will be
the power factor less will be the load currnt.So power
factor should be maintained 0.97 to 0.99

Is This Answer Correct ?    9 Yes 1 No

What power factor maintain you maintain at u r organisation..

Answer / er. dattesh shah

0.999

Is This Answer Correct ?    5 Yes 1 No

What power factor maintain you maintain at u r organisation..

Answer / ashish rai

It should be near to one(less than one) . but not to one.
For stability static device has come which control the
capacitor bank automatically. So there is no problem of
stability . If anyone are going for the small industry , he
should try to maintain it near to .95. .80 is not so
effective power factor now a days. It can be acceptable for
home application not for the industrial purpose.

Is This Answer Correct ?    5 Yes 2 No

What power factor maintain you maintain at u r organisation..

Answer / vishok

It should be close to 0.8.

Is This Answer Correct ?    11 Yes 9 No

What power factor maintain you maintain at u r organisation..

Answer / harish

and same here to, we maintain of power factor of .8 or .9,
must close to that

Is This Answer Correct ?    5 Yes 3 No

What power factor maintain you maintain at u r organisation..

Answer / william lobo.

We maintain 0.8 and above since we are penalised by KEB for
low pf. we generally maintain close to 0.9 by use of power
capacitors. Too high i.e. above .95 is too costly to
install and also the problem is that if power factor is
close to 1 then there are chances of high voltage affects
motors and we suffer more motor burning at our plant.

Is This Answer Correct ?    1 Yes 0 No

What power factor maintain you maintain at u r organisation..

Answer / sandeep lole

In industries, mostly the loads are inductive type. So the
PF is low near about 0.8 lagging. Due to that the load
current is maximum.We can improve the PF by using Capacitor
bank in industrial substation. So that we can improve Pf
upto 0.99. For that proper design of capacitor bank is
important.

Is This Answer Correct ?    2 Yes 1 No

What power factor maintain you maintain at u r organisation..

Answer / manish singla

I have always maintained Power Factor 1 (Not Leading Nor
Lagging) during my days with Maintenance Deptt.

Resulting in saving of Atleast Rs40k in monthly bills,
Better Voltage etc.

Is This Answer Correct ?    0 Yes 0 No

What power factor maintain you maintain at u r organisation..

Answer / manish singla

In our state we get Incentive for maintaining Power Factor
over and above 0.90 Lagging till Unity.

Secondly, Maintaing Power Factor at Unity keeps your
distribution system healthy resulting in low line losses
within your premises as well inputs of your premises.

This is wrong statement that it will lead to burning of
equipments and premature failure of electrical equipment.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

dear all, in motor operation , motor is of 100 hp and bimetal relay setting is 130 amp, if relay is getting tripped on 120 amp balance current what can be the reason? Relay is newly replaced. I dont know but is there any frequency effect in thit case? Can frequency variation affect bimetal relay operation?

1 Answers  


Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?

0 Answers  


What is the function of wave trap in an electrical substation?

2 Answers  


How we can convert H.P into KW or Vice versa

11 Answers   Suzlon,


Why transformer rating is represent in KVA?

7 Answers   Bhel, Sonalika, Usha Martin, Wipro,






my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?

1 Answers  


What is the classification of hydro projects based on installed capacity?

0 Answers  


what is the meaning of DSL

4 Answers   Airtel,


In simply words(not explain any formula )what do you mean by power factor.?

5 Answers   DRDO,


how to find under ground cable fault ??? if our cable size is 95*4 then what will load capacity with far mull

2 Answers   Imdad,


why induction motors are of lagging type and not leading type

9 Answers   Bhel,


the need of star to delta anddelta to star

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16636)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)