When charging a 20 MVA , 33kV/6.6kV transformer through
regulated (0-6.6 kV or 0-33 kV) source on no load , what
will be the maximum current drawn by transformer from
source and what sould be the source capacity.
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
Actually above answer is not correct as it is the full load
current.No load current is approximately 4 to 5 % of rated
full load current. hence considering the terminals (i.e HV
side or LV side) the current drawn from source will be 4 to
5 % of respective side rated current.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / satya
the charging current is about 6 times the full load current
about 2000 amps but that will be for mill seconds
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gunasekaran
for good transformer it should be 0.5%of full load current
for normal it may be upto 1%
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / pulkit
max current when on load wil be 390 amp drawn by the Hv wdg
of t/f and when on no load the transformer primary losses
occur on the basis of elctic flux principle in which when evr
the current flows in a loop,there is loss in the form of
magnetic field energy that is created arround the primary
coil.it is 1 % of the hv wdg current.
| Is This Answer Correct ? | 0 Yes | 0 No |
difference between analog pressure gauge & digital pressure gauge?
how to calculate P.F from kva only?
What is the use of iron core in a transformer?
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
Why armour HT XLPE power cable required to Earth?
what types of load we get from the national grid? is this capacitive or inductive?
Is phenomenon of resonance is harmfull fr the machine? if not or if yes please explain it?
explain Uninterrupted power supply detailed electronical operation with circuit diagram
what is meant by slip & where its occur ?
What is DC power factor??
if we appling capacitor at above rated what are looses and what will be happen
4 Answers Radiant, Real Estate,
What does OHB stand for in specifications for circuit breakers, especially found in SF6 circuit breaker?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)