When charging a 20 MVA , 33kV/6.6kV transformer through
regulated (0-6.6 kV or 0-33 kV) source on no load , what
will be the maximum current drawn by transformer from
source and what sould be the source capacity.
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
Actually above answer is not correct as it is the full load
current.No load current is approximately 4 to 5 % of rated
full load current. hence considering the terminals (i.e HV
side or LV side) the current drawn from source will be 4 to
5 % of respective side rated current.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / satya
the charging current is about 6 times the full load current
about 2000 amps but that will be for mill seconds
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gunasekaran
for good transformer it should be 0.5%of full load current
for normal it may be upto 1%
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / pulkit
max current when on load wil be 390 amp drawn by the Hv wdg
of t/f and when on no load the transformer primary losses
occur on the basis of elctic flux principle in which when evr
the current flows in a loop,there is loss in the form of
magnetic field energy that is created arround the primary
coil.it is 1 % of the hv wdg current.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the formula to find out how many amps generater takes running on full load.
why electrical power has benn needed for speed controller of woodward governor control for biomas power plant
What is EHT tariff or Power factor Tariff ????
how to maintain frenquncy with syncronising sub-station for distribution
xfhnchncv?
what is PWM in IGBT and how it works for drive.?
What is the actual calculation for transformer short circuit test?.
grr resistance & contrator malt continuous
why ct ratio always rated 5.
why the Parameters : Base Voltage & Maximum Voltage can't be equal in value in a VFD (Variable Frequency Drive) ? How much the base voltage would be lower than the maximum voltage ? If 400 V is the 3 phase output of a VFD ... then what should be the base voltage ? thanks a lot
why buchholz relay installed in inclined position
What is the power factor of an alternator at no load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)