what is impedence (Z) of transformer, what indicate in
transformer , which perameter indicate in transformer
Answers were Sorted based on User's Feedback
Answer / jay
Impedence is the composition of Resistance and Inducatance
of the transfromer.
And inductance should be 5% of the transformer rating.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / abdul wajid
The impedence (z) of Transformer is the total resistance
offered by Transformer .Transformer is indicated by its
losses iron and core losses
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sivaramakrishnan.s
You can see the %impedance in the nameplate details.
Transformer designed depend on the full load Current.
Actually.. How much %primary voltage required to flowing the full load current at secondary side when secondary is short circuited called as %imp volt in transformer. It will be %volt of Transformer primary voltage..
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sunil ulange hit belgaum
THE VOLTAGE DROP RESULTING FROM REFERENCE CURRENT AS
PERCENTAGE OF REFERENCE VOLTAGE IS CALLED IMPEDANCE
| Is This Answer Correct ? | 3 Yes | 1 No |
transformer is always interposed between a primary source
of energy and a secondary that makes use of that energy.
Hence, the transformer constitutes an impedance to current
flow from source to load. The higher that impedance, the
more voltage drop will occur for a given load current. If a
secondary fault occurs, its effect on the circuit will be
lessened to the extent that transformer impedance
increases. The circuit designer therefore needs to know the
value of transformer impedance.
| Is This Answer Correct ? | 2 Yes | 1 No |
What is the electrical difference between Earthing Switch (ES) and Maintenance Earthing Switch (MES)?
what is the power ratio between power in star and delta circuit?
Pls mail me utility & Dg related question with answer
why they were using TRIAC instead relay in some controllers and what is the advantages.
Which ciass CT can be use in diff. protection. Can be use 5p20?
what is per unit calculation?looking for simple and strong explanation thk u
To have variable speeds we use a. Induction motor b. Traction motor c. Shunt motor
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
how many types of motor can be used in washing machine
what efficiency of transformer at 100% load
How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)