Why the rating of the HT breakers are in 1250 Amp, while
the load on the breaker is around 50 Amp. ?
Answers were Sorted based on User's Feedback
Answer / sobhuza, za
For those who this my answer (Answer 2) is incorrect. It is
important to remember that HT circuit breaker has two
current ratings. One is the continuous current rating. The
other one is the maximum fault breaking rating that the
breaker can carry for about say 2 seconds. The former is
what the question is about. The latter is in kA range
typicaly 25kA or so. Therefore 1250A is just a normal load
current that the circuit breaker can carry.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / rahul
bcoz CBs are supposed to interrupt fault current which can
be several times larger than the continous load current.
( for further clarification see CB specifications)
Is This Answer Correct ? | 21 Yes | 11 No |
Answer / shan80
there is no necessery to use 1250 vcb for 50A u can use
630A vcb for that load.1250A is only manifaturing capicity
630A vcbs also available and these rating r standard. 1250A
rating is only normal current rating not shot circuit rating
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / vikash kumar
HT breaker is sized based upon the fault current. Here 1250A is the fault current. 50A is the normal current and overload protection is provided by CT and over current relay.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / arjun
it is coz the voltage at the HT side is much high & so is the pressure of the voltage is also much high, therefor the selection of the HT breaker depends on various other factors such as pole distance(distance between the poles of the breaker ) ,voltage (The voltage rating of the circuit breaker must be at least equal to the circuit voltage.), ambient temperature,overload,continuous current rating & max current it can handle before tripping .so even if the current though a HT circuit is low we need a breaker of much higher ratting
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / v.v.j.rao
The rating of the breaker current 1250 means it can carry
1250 amps after that % over loaad depends on O/Load setting
of 50%,75% or 100% only.If you put this breaker at 50 amps
oad this will not trip under any O/L condition of that
particular load.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sobhuza, za
It's because the equipment is rated based on the capacity
levels and not at loading levels. CB ratings are
standardised, as it may happen that the loading on one
circuit is 50A, but on another it can be 900A. So for
rating purposes it is better to standardise at say 1250A so
for ease of procurement. Remember that when the load
increases over time and you won't have to change CBs due to
loading increase.
Is This Answer Correct ? | 11 Yes | 16 No |
Answer / sbb
It is because we cannot measure the high current directly.So
for this we will keep CT's to measure high currents.In
primary side it will be 1250A and in secondary side it will
be 50A,this is nothing but CT Ratio.
Is This Answer Correct ? | 1 Yes | 16 No |
how to calculate the load on transformer..????
I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel of 400 kVAR(LT).Now if i want to remove the LT APFC panel and install a HT(11kV) APFC panel on the HT side is the HT APFC panel will work same as the LT APFC panel(improve the power factor),if yes what will be rating of the HT APFC panel?what is the formula to calculate HT APFC panel rating???
What is mean by hot and cold loop testing? What is the difference between them?
HOW TO DESIGN THE body EARTH cable(Copper Conductor) size for 60KVA UPS?
How to calculate energy stored in an inductance?
. Is there a simple method to measure the horsepower of a small motor (1-3 hp) for a non-technical person
what is rotor earth fault protection scheme in hydro generator & what is dc field flashing ?
Why we are using Ohm's law? where it is applicable? explain.
10 Answers Pyramid Saimira, TCS,
What are the types of transformers according to the arrangement of iron cores?
How phase displacement change in the over current relay coils.
In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..
Is it possible to power factor more than unity?