Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why the rating of the HT breakers are in 1250 Amp, while
the load on the breaker is around 50 Amp. ?

Answers were Sorted based on User's Feedback



Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / sobhuza, za

For those who this my answer (Answer 2) is incorrect. It is
important to remember that HT circuit breaker has two
current ratings. One is the continuous current rating. The
other one is the maximum fault breaking rating that the
breaker can carry for about say 2 seconds. The former is
what the question is about. The latter is in kA range
typicaly 25kA or so. Therefore 1250A is just a normal load
current that the circuit breaker can carry.

Is This Answer Correct ?    17 Yes 3 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / rahul

bcoz CBs are supposed to interrupt fault current which can
be several times larger than the continous load current.
( for further clarification see CB specifications)

Is This Answer Correct ?    21 Yes 11 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / shan80

there is no necessery to use 1250 vcb for 50A u can use
630A vcb for that load.1250A is only manifaturing capicity
630A vcbs also available and these rating r standard. 1250A
rating is only normal current rating not shot circuit rating

Is This Answer Correct ?    7 Yes 5 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / vikash kumar

HT breaker is sized based upon the fault current. Here 1250A is the fault current. 50A is the normal current and overload protection is provided by CT and over current relay.

Is This Answer Correct ?    0 Yes 1 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / arjun

it is coz the voltage at the HT side is much high & so is the pressure of the voltage is also much high, therefor the selection of the HT breaker depends on various other factors such as pole distance(distance between the poles of the breaker ) ,voltage (The voltage rating of the circuit breaker must be at least equal to the circuit voltage.), ambient temperature,overload,continuous current rating & max current it can handle before tripping .so even if the current though a HT circuit is low we need a breaker of much higher ratting

Is This Answer Correct ?    3 Yes 5 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / v.v.j.rao

The rating of the breaker current 1250 means it can carry
1250 amps after that % over loaad depends on O/Load setting
of 50%,75% or 100% only.If you put this breaker at 50 amps
oad this will not trip under any O/L condition of that
particular load.

Is This Answer Correct ?    1 Yes 4 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / sobhuza, za

It's because the equipment is rated based on the capacity
levels and not at loading levels. CB ratings are
standardised, as it may happen that the loading on one
circuit is 50A, but on another it can be 900A. So for
rating purposes it is better to standardise at say 1250A so
for ease of procurement. Remember that when the load
increases over time and you won't have to change CBs due to
loading increase.

Is This Answer Correct ?    11 Yes 16 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / ajay

I think it is according to its circuit breaking capacity at
fault, that how much current it can bear durring breaking
of curcuit

Is This Answer Correct ?    3 Yes 13 No

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp...

Answer / sbb

It is because we cannot measure the high current directly.So
for this we will keep CT's to measure high currents.In
primary side it will be 1250A and in secondary side it will
be 50A,this is nothing but CT Ratio.

Is This Answer Correct ?    1 Yes 16 No

Post New Answer

More Electrical Engineering Interview Questions

What is the minimum permissive IR value for LT & HT motor for safe starting?

1 Answers   Rukmani,


why two point starter,three point starter, four point starter cannot be used for A.C machines?

2 Answers  


what is the resistance value of earthing pit and why they are connected?

6 Answers  


In a single phase converter, the no. of SCR conducting during overlap? a.1 b.2 c. 3 d. 4

3 Answers  


When the DG is running at the time we can connect to capacitor banK? why it is required or not

1 Answers  


a solenoid of inductance 250mH and resistance 10ohm is connected to a battery. the time taken for the magnetic energy to reach 1/4th of its maximum value will be?

1 Answers   SSC,


what is function of reactor coil in Power factor correction panel

1 Answers  


Why fuel tanks to be earthed ?

6 Answers   Electronics, Hindustan Petroleum, HPCL, Ispat,


what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up

1 Answers  


What is the cause for a blown fuse in one phase of primery side(HV) of a three phase transformer( 4169v-460v) in the time of closing its supply breaker. There is no load on the secondery side of the transformer in this moment.

3 Answers   Novachem,


what is the reason of current flow in nutral although load is balanced (three phase equal current)

3 Answers  


Which lamp will fuse first(1)20(2)40(3)200 three lamps will fuse together

2 Answers   NTPC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)