what is the differance of acb and mcb and mccb
Answer Posted / shiva.sh
mcb-miniature circuit breaker- 6amp to 100 amp
mccb-moulded case circuit breaker- upto 1000 amp
acb- air circuit breaker- above 6000 amp
| Is This Answer Correct ? | 0 Yes | 2 No |
Post New Answer View All Answers
in dc shunt motor if field winding is shorted then
What is slope...? Explain slope 1 and slope 2...?
What is gain margin?
What are the material used for resistor?
why we are using Load factor?
can the measured percentage error during calibration of single phase energy meter be negative?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
What are root loci?
How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.
List advantges of active filter over passive filter?
IN SINGLE PH TRANSFORMER IF LEKAGE IMPEDANCE DROP IS NEGLECTED ,THE FLUX IN THE MAGNETIC CORE and the lekage flux linking a winding are a)proportional to the applied v to the winding i respectively.
How to calculate impedance volt in Transformer?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
which metal is use in shunt