6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
| Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
| Is This Answer Correct ? | 1 Yes | 5 No |
1. transformer design formula ? 2. how to calculate the primary turns and secondry turns ? 3. core types ? 4. how to find the primary current and secondry current ? 5. how to calculate the stacking factor ? 6. range of fulx density ?
2 Answers Automation, Indian Railways, Mogora Cosmic,
what is transient enclosure vltage , very fast transients, very fast transient over voltages
what is different between installation and commonissonig.
1. what is the power factor and whatis his losses 2. what is the working procedure of 51RNB AND 87 relay
What is the make of breakers, transformers, generators? What are their capacities and ratings?
how electricity is generated through electeic generator ?
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
6. A DC AMMETER HAS R=0.1 OHM & CURRENT RANGE IS 0-100 A IF THE RANGE IS TO BE EXTENDED TO 0-500 A THEN METER REQUIRES SHUNT RESISTANCE OF ..........
Whats the difference between three phase and single phase?
Earth bits close or open. Which is correct
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
Which Motor used in Fan's Motor ?
3 Answers Matsui Technologies,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)