6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
| Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
| Is This Answer Correct ? | 1 Yes | 5 No |
How can be decreased the size of transformer?
if you short the any 2phase(R,Y,B),why fuse get blown?
if we want to convert the two 12 V DC batteries in parallel for UPS ? what would be the result ? which is better for a UPS , connect two batteries in series or connect them in parallel ?
I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
what is the purpose of %impedance for transformer
Q. calculate the value of the resistor to be connected in series with a 100W; 230V lamp so that the wattage of the lamp is reduced to 35W
how to check a transformer insulation?
3 Answers Kirloskar, Kirloskar Chillers,
What we change frequency from transformer. yes or no
In DC while we mention the voltage we are using -48V but in case of AC we mention only 230V not -230V, why we using -48V not 48V
The sodium vapor lamp is not glows when it is connected a distance of 5 meters above from gearbox, why ?
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
where used of HVDS system.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)