6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / rvg

The transformer details shows no load voltage and we can
assume about 3-4% decrease with full load. ACB with rated
voltage 690 should not be suitable for 725V. ACB's nominal
voltage should be 1.414 time the applied voltage.

Is This Answer Correct ?    6 Yes 2 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / mnm

Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.

Is This Answer Correct ?    1 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / praveen kumar gupta

ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.

Is This Answer Correct ?    0 Yes 0 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / loke

We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.

Is This Answer Correct ?    0 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / joe

there wil be no effect because in transformer the input and
the output is difference due to the coil winding

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

what are iron and copper losses

4 Answers  


what is the difference between delta delta and star delta connection transformer? why we use delta delta transformer since it need earthing transformer for grounding?

0 Answers  


basic princple of induction and synchronous motor

1 Answers  


Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?

0 Answers  


is there any lightning by passer is arranged in ship like buildings?

0 Answers  






Multi-step core is used in transformer to: A) Increase the output B) Decrease the cost of core material C) Decrease the cost of copper D) Increase the efficiency

1 Answers   Accenture,


what is meaning of AMF, WHY IS USING IN GENSET

1 Answers  


How to Convert horsepower to kva? what is the three phase formula? email me if u know thanks Rehan smileavail@msn.com

3 Answers  


What is a captive power plant?

2 Answers  


how to get 48 V DC I have ... 1. 12 volt power supply board 2. DC power supply ( max. 30 v) 3. 9 volt batteries ( 2 - not chargeble)

2 Answers  


Hello seniors m an engineering student in 3rd yr..i want to know what are the software course in electrical field?i wanted to do certification course but i dont know much about the course?..Regards

0 Answers  


As per standard, transformer body earthing and other Equipment earthing (Equipment earthing) did not connect. but in LT side termination we are doing metal glanding in both side Transformer to PCC Panel through armoured cable, now X'mer body earthing and PCC Pane earthing (Equipment earthing) both are connect.is this safe for X'mer or other equipment?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)