6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
Is This Answer Correct ? | 1 Yes | 5 No |
Define Current Transformer? Working & TYpe's Of C.T.
for same rating of a transformer and induction motor which one will have higher magnetising current flowing?
When connecting a loaded powerplant to the Huge grid,what are the factors to be considered and how the VAR flow will affect the system?
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
i want prepare power grid exam what are book we want refer for electrical ?
WHY STABILIZER SHOULD USED
What are the RGGVY, APDRP, RE?
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts same result on 24Volts and with ground 12Volts only expert answer that thanks we can not ground the battery.
What is mean by voltage & current.
Why have the transformer one earthing to their neutral? Why have the transformer many earthing to their body?
Vibromotor 252MV 1/4HP2P..what is mean by 252MV?
Which type starter is used for synchronous motor?