Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?

Answers were Sorted based on User's Feedback



6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / rvg

The transformer details shows no load voltage and we can
assume about 3-4% decrease with full load. ACB with rated
voltage 690 should not be suitable for 725V. ACB's nominal
voltage should be 1.414 time the applied voltage.

Is This Answer Correct ?    6 Yes 2 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / mnm

Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.

Is This Answer Correct ?    1 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / praveen kumar gupta

ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.

Is This Answer Correct ?    0 Yes 0 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / loke

We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.

Is This Answer Correct ?    0 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / joe

there wil be no effect because in transformer the input and
the output is difference due to the coil winding

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

what is SWA type of cable?????

4 Answers  


Explain Active power,reactive power,how its related to each other , & inductive ,capacitive.

0 Answers  


What is the difference of grounding and earthing?

6 Answers  


What is maximum load capacity of 800 VA inverter?

5 Answers  


why earthing is not required on transformer prymary winding side ???

13 Answers   Genpact,


how to calculate percentage impedence at 75 deg C at normal tap

0 Answers  


what is the difference between STAR and DELTA connection and application wise how it can be utilizedd ???

1 Answers  


In DC current-excitation to transformer, why it sucks more current? Eventhough there is no power transfer between primary and secondary? R is very low so it should suck less current only na thn y its current increases?

2 Answers   Cairn,


describe the fully control circuit diagram of ac drives

0 Answers  


how capacitor pass ac voltage practically?with increase frequency and cpacitance?

1 Answers   DELL,


how to protect transformer

2 Answers  


why we don't use earthing as neutral?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)