What is the d/f between DOL & star delta starter & automatic
star delta starter?
Answers were Sorted based on User's Feedback
Answer / prakash
A DOL starter connects the motor terminals directly to the
power supply. Hence, the motor is subjected to the full
voltage of the power supply. Consequently, high starting
current flows through the motor. This type of starting is
suitable for small motors below 5 hp (3.75 kW). Reduced-
voltage starters are employed with motors above 5 hp.
Although DOL motor starters are available for motors less
than 150 kW on 400 V and for motors less than 1 MW on 6.6
kV. Supply reliability and reserve power generation
dictates the use of reduced voltage or not
To reduce the starting current of an induction motor the
voltage across the motor need to be reduced. This can be
done by autotransformer starter, star-delta starter or
resistor starter. Now-a-days VVVF drive used extensively
for speed control serves this purpose also.
| Is This Answer Correct ? | 492 Yes | 65 No |
Answer / niranajn
in dol starte the motor is directly fed from the line and
in star delta starter ther motor is started initially from
star and later during running from delta
| Is This Answer Correct ? | 348 Yes | 49 No |
Answer / suresh pulipati
In case of Star Delta starter the motor intially will run
in star connection and when 80% of rated speed picks, the
motor change over to delta connection. With this star delta
connection we are able to reduce starting current by 1/3 of
DOL starting current and starting torque also.
| Is This Answer Correct ? | 226 Yes | 33 No |
Answer / cool
Whenever you start a big heavy electric motor, you need to
start it slowly to prevent the rotor overheating and
drawing an enormous current. When the windings of a 3-phase
motor are connected in STAR the current is reduced to only
root three of the normal running current that is taken when
it is connected in DELTA.
| Is This Answer Correct ? | 141 Yes | 19 No |
Answer / ankur mishra(moradabad)
In DOL starter full line voltage is fed to motor which will
start motor with a shock, it also draws very high current
than rated current(around 6 times), but if we use star-
delta starter , the motor starts as a star connection later
which is converted in to delta.
using star connection the line voltage is devided in two
phase voltages, also impedence is also increased due to two
star windings which result in low starting current and low
torque which will prevent motor to run with shock.
another difference is DOL starting takes less time while
star-delta takes more time to run at rated speed.
| Is This Answer Correct ? | 91 Yes | 13 No |
Answer / honey
in induction motor the torque is propotional to squre of
supply voltage in case of dol the motor directly connected
to supply so torque is more while in star delta the motor
is firstly connected to star hence voltage is reduced
torque will be less and when motor reaches its 80% of speed
it connects with delta with the help of timer then full
voltage is supplied hence less rating motor should be
started with dol but for high rating it should be with star
delta
| Is This Answer Correct ? | 58 Yes | 8 No |
Answer / dipanshu singh
in dol motor is supplied full line voltage hence torque
will be more, whereas in star delta the voltage is reduced
by root 3 times hence torque reduced
| Is This Answer Correct ? | 51 Yes | 15 No |
Answer / vasu.p
in dol starter the motor is directly fed from the line and
in star delta starter then motor is started initially from
star and later during running from delta
| Is This Answer Correct ? | 43 Yes | 7 No |
Answer / electo man
To the point, when motor starts using DOL it takes 6 times
its rated current to just start. while in Star-Delta
starter its starting current reduces to one by root three.
| Is This Answer Correct ? | 47 Yes | 18 No |
Answer / rajendra mallick
In a DOL starter motor terminals is directly connected to
starter such that initially a very high starting current is
feed to drive the motor.Dol starter is used for small
motors below 5hp because of high starting current may
damage motor winding. Dol starter using for large motor
using star delta connection,first motor run on star
connection mode upto 80% which provide low starting current
and low torque initally and after getting maximum torgue
motor operates on delta mode with high torgue.
| Is This Answer Correct ? | 25 Yes | 6 No |
In sub-station how to find multifactor of panel?
HOW THE OLTC TRANSFORMER SAVE ENERGY IN COMPARISON TO OFF LINE TRANSFORMER AND IS IT ECONOMICAL TO REPLACE THE OFF LINE TRANSFORMER TO OLTC TRANSFORMER
how point on wave controller works.
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
what is relation between voltage and current and don't take resistance here. if we supose say when there is increase in voltage whwt happens to current?is it decrease or increase?
What is the difference between line drop and percentage line drop?
what is the function of turbo charger in disel generators
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
What are hrc fuses and where it is used?
what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
Dear sir/mam Iwant complete details of Naintenence of 33kv/433v Transformer having 1250 KVa
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)