what is advantage in open delta connection?
Answers were Sorted based on User's Feedback
Answer / iqbal ahmad
The very useful advantage of open delta connection is to
detect ground fault at any bus or line of a system. usually
open delta connection transformer is used in potential
transformer to detect ground fault as a 3rd core of PT.
Is This Answer Correct ? | 66 Yes | 20 No |
Answer / swapnil
with use of open delta connection maintenance of
transformers is possible . If load on two transformers
increase than we can install another transformer and close
the delta in future .
Is This Answer Correct ? | 45 Yes | 12 No |
Answer / sam khanji
open Delta will supply 57% if its rated value and give the
apportunity to increase the ratio by adding the missing leg
to become a complete delta.
Is This Answer Correct ? | 38 Yes | 16 No |
Answer / niranajn
An open delta connection can supply power at 53.3% of its
rated value.
Is This Answer Correct ? | 46 Yes | 27 No |
Answer / derekdejs64
In three phase system it use for Directional Earth Fault
relay voltage element.
Is This Answer Correct ? | 38 Yes | 21 No |
Answer / dnyaneshwar
in unearth sysytem open delta connection is used for
detecting of earth fault & single phasing of equipment.
plz, anybody give another ans......
then welcome.
Is This Answer Correct ? | 40 Yes | 30 No |
Answer / imtiaz khan
There are two biggest advantages:
1) In an unearthed system like capacitor banks, it is possible to detect ground faults though earth path is not available.
2) In case of bulk power transmission where transformer banks are used, their advantage is that if one leg is out for maintenance/replacement than also approx. 57% power can be transmitted.
Is This Answer Correct ? | 14 Yes | 4 No |
Answer / subhankar nath
By the open delta connection of PT we can monitor the
neutral shifting of the system as well as it can be use in
the genetating end substation for the maintenance of the
transformer in the time of low load demand.
Is This Answer Correct ? | 18 Yes | 11 No |
Answer / hitesh gohil
An open delta connected when full power is not needed.
Is This Answer Correct ? | 16 Yes | 13 No |
Answer / ram
Open Delta Connection Means Potenial Transformer Secondary
Series Connection Was Given,And Grounded.This Line Was Zero
Potenial,When Voltage Flow For This Line Open And Trip The
Relay.Unbalace Voltage Came Also Trip The Ckt.
Is This Answer Correct ? | 3 Yes | 0 No |
what is the advantage of using 3 phase line rather than using 2 phase line?
11. As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why? 12. How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test? 13. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV? 14. Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it? 15. Explain why the Voltage drop will happen in 3 Phase line? 16. What is the equipment used to control the generator output? 17. What are the factors to be considered during the Synchronization? 18. What should be value of Circuit breaker operating time and tripping time? 19. Why the CT Secondary is rated as 5A generally? 20. At which time Synchronous generator act as a Synchronous Condenser?
HOW DO WE COLLECT THE SOLAR ENERGY AND DESCRIBE THE METHODS TO CONVERT THE SOLAR ENERGY INTO ELECTRICAL ENERGY?
WANTCONTACT NUMBER & EMAIL/ WEBSITE TO CONTACT THE SECRETARY,MADHYA PRADESH LICENSING BOARD(ELECTRICAL),K- BLOCK,3RD FLOOR,SATPOODA BHAWAN,BHOPAL
what kind of motor is used for lifting applications
how to decide the panel size like MDB ,SMDB PANEL SIZES
What is the method of Tan delta test for power Transformes and why it is required.
first 3 men were there .again 3 came.total how much?
i have some screw comprressor with 630kw power,i have established them with simple star to delta circuit,by the way there is so much inertia when the screw comprressors start, can you offer me contactors power with 400vac or any cataluge to choose the contactors
the distance from my office to d.g is aprox 400mtrs and voltage drops ibn my office near about 40 volt what should i do p[ls suggest.
Which Current transformer will be bigger in size, 400/5 or 400/1 & why?
what is smartµ grid technology?under coal gassification?