How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answers were Sorted based on User's Feedback
Answer / rasel-amie
HT Cable select, its depend of incoming capacity of feeder
line. say feeder capacity 100 MVA SO Calculate current I=
100*100/11*1.73=5.25kA. So we can select of HT Cable for
minimum short ckt current carrying capacity of minimum 5.2kA.
| Is This Answer Correct ? | 10 Yes | 14 No |
Answer / er.rupam dwivedi
A=kva x 1000/1.732x ht voltage=ht cable selection
| Is This Answer Correct ? | 2 Yes | 6 No |
Answer / govind bisht
Assume PF of transformer is .8.
rating of transformer=1500kVA=1500X.8=1200kW
V=433(3phase)
So that maximum current-
I= P/V*PF
=1200*1000/1.732*433*.=1600A
So cable size required if copper cable
1mm=4amp= 400sqmm(by consedering all factors)
For aluminium cable
1mm=2.5A=640sqmm
| Is This Answer Correct ? | 61 Yes | 109 No |
Answer / m.jagadeeshwar
for 11kv side current = kva*1000/1.732*11000
= 78.73 amps
for 78.73 amps 3 core 25 sqmm cable is sufficient
| Is This Answer Correct ? | 22 Yes | 84 No |
Explain and give examples about VCB?
0 Answers AZ Engineering, Vodafone,
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
How to convert 110 volt alternating current to 12 volt direct current
show the single line diagram of star delta starter with single phase preventer
can we install HT panel & LT panel side by side or how much clearance is required ?
what is difference between c-power & u-power air circuit breaker?
2 Answers Areva, IIT, Marine Electricals,
What kind of preventive maintenance are there for AC induction motor?
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
Just a silly question but just to make my curious mind bac to normal - Why was not 67 and 67N relays built into a single relay as i have noticed that the R,Y,B CT wiring end up into the 67 relay while the common of the R,Y,B CT wiring end up into the 67N relay. Then it was better if a single relay was manufactured just like the distance relay (21). Another question i would like to ask is - how do we know where the 67 and 67 N relay has to be placed.why is it not placed at the transformer bay? In the substaion that i am working -i have noticed that it is placed between a breaker and a common double bus bar and this line bay is connected to another substation at a remote place which is furthur connected to a load. B U S______CT for 67 & 67N ______Breaker _____ remot s/s. B A R
What is voltage ratio of a transformer?
How to calculate the Airconditioner capacity for a standard telecom BTS shelter?
What is the current carrying capacity of 1.5 rm and 2.5 rm cable
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)