How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answer Posted / engr. md n h shabuj
S=(Ish *√t)/K
=(10.49*√1)/0.143
=73.35
=75Rm cable
Ish =P/ (√3*V* % of Z)
= (1500*10^3 )/( √3*11*10^3*7.5%)
=1049A
Ish =1049*10=10490A=10.49KA
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
how many safety really of DG sets.
Classify driling machines.
There are Two questions about Steam Turbine Generator... What is HRSG bypass of LP, HP used for in power generation? In particualar, in the event that fault of HP bypass, there would be STG TRIP in operation but none on the LP bypass fault...what's the reason ?
DG Earth Value?
State and define norton’s theorem?
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
What is the difference between DOL starter and star delta starter
can we find the inductance of a induction motor?
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
Differnce between negative Pahse SequenceFunction and unbalance Function?
What is the maximum percentage voltage drop (vd%)for a motor control center
show the single line diagram of star delta starter with single phase preventer
What are dependent sources?
What is an ac motor?
what are the steps involved in generator load test?