How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
If the load is 100 A ,the meter records correctly if the CT ratio is 100/5 as the meter gets 5A current . If the CT ratio is 600/5 the current in the meter will be 5/6 A for the same load current . Hence to get the correct reading ,multiply by 6.
| Is This Answer Correct ? | 8 Yes | 2 No |
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
what is the full name of ELCB &MDB <MCB
Can I Drain A Oil For Sample When The Transformer is Running? (Charged)
how to identify the cable quality and what is flame proof cable
In a transformer ,when voltage decreases current increases. but this is a violation of oms law.why?
all interview questions with answers of ntpc (2000-2009
How To Convert Apparent Into Real Power Without Knowing Reactive Power?
IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace.
how to calculate the lightning arrester conductor @ no of earth pits required
Do I need a special Transformer to put 240 VAC 3 phase into it and and get 480 VAC 3 phase out of it to run a machine? Or, do I just use an ordinary step down transformer and step up the voltage? Thanks
what is load balancing. what maximum load diffence is allowed between phases.
what is the voltage and ampere rating of all range of HT conductor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)