kindly tell me how the load on generator increase by just
increasing the fuel of prime mover, as if for exampple 20
MW gen set is synchronized the load ramps from zero to 20
MW gradully and during this procress only fuel of prime
mover increases. Which thing determines the load on
generator with respect to fuel
Answers were Sorted based on User's Feedback
The load on the generator means,the line current draws from
the generator. Pls be remind that, generator is an energy
converting device, which converting mechanical energy to
electrical energy.
As soon as more current draws from the generator,the
mechanical load on the prime mover also rises. SO that, more
fuel consumption takes place.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / haribabu dasari
Any alternator share load depend up on load angle . If we
increase fuel of prime mover , prime mover drives
alternator advance in load angle ,due to this, alternator
shares more load (load is constant so load sharing between
generators only posible).if you want to load generators
you have to switch on the load switches.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / j.kesavan
fual consumption is depending upon the load.and speed of
the primovers.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagesh
GOVERNOR IN THE FUEL PUMP DETERMINES THE LOAD OF THE ENGINE
WITH RESPECT TO SPPED OF THE ROTOR.
Is This Answer Correct ? | 0 Yes | 3 No |
We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?
why indicated sypply only by 440V in 3-phase system.
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
why we use to transmit the power in three phases intead of single phase ?
what is a DLC?[just dont reply its a Dual loop controller!] Plz do Explain the advantage of DLC over PLC?
I have a reading off 1.5ohms at my mem my main c/b is rated at 40/6 amps in a domestic house and i was told to change it to a b curve c/b is this ok
how to calculate the current capacity of a wire if its dimension in Square mm is given
A heater capacity is 3.0 KW on 415V . if supply voltage is 380Volt . what is heater capacity on 380volt . and how calculate and give formulas . Prakash veer singh Roto power Engg.
why earthing is not required on transformer prymary winding side ???
Sir, I completed DEEE... And now I working in TNEB for one year apprenticeship. If I eligible for applying c license and how can I get?
i want to model paper for section engg.
What is 100% protection of generator? Why 100% is not used but 95% is generally used?