When geneartor is running in poor lagging side power factor
its excitation current increases then it is running in
improved lagging side.Kindly tell me when gen is running in
leading side what will happen
Answers were Sorted based on User's Feedback
Answer / asif raza
MY DEAR FRIEND AS WE KNOW THAT, ALL GENERATOR ARE DESIGN TO PRODUCE THE POWER WITH LAGGING P.F,SUPPOSE IF WE INCREASE MORE EXCITATION CURRENT TO THE GENERATOR'S ROTOR FIELD, THE P.F WILL BECOMES LEADING & ARMATURE REACTION WILL TAKES PLACE DUE TO THE EFFECT OF STATOR FLUX ON ROTOR FIELD.SO YOUR AVR WILL LOSSES THE CONTROL OVER ALTERNATOR & YOUR WINDING WILL DAMAGE.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / naveen
your question is confusing, specify lagging or leading.
if generator running in leading PF then increase exitating
to bring it to lagging region, because it is ment for
lagging power factor only
if it is running in leading then chances of generator
failure are more,but before that generator protection will
trip.
| Is This Answer Correct ? | 0 Yes | 2 No |
When generator is running in leading side then the
excitation current should decrease to improve the pf....
| Is This Answer Correct ? | 0 Yes | 3 No |
Can we convert off load tap changer transformer to on load tap changer transformer
we all know voltage is a force(emf), and the force always devides if 2 or more than2 loads are there but why does the voltage remains same is parallel, it must devide na ???
what will be the motor terminal box connection arrangement (star or delta). on what basis it decided?
how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?
3 Answers Megatron Solutions, TCS,
Can you explain about pole discrepancy scheme
what is the chemical name for oil that used in the transformer
in star delta starter current is 1/3times the delta value how?
what is the formulae of calculating voltage drop?
why we generate transmit and distribute electrical supply in multiple of 11
How to see the inductance in a transmission lines
We have 90mX100m hangar with 16 no.of supporting pillar. It is required to provide power supply on all pillars. what is suggested earthing scheme for hangars.
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)