generator(Deutz 550kv)is runing for 2 hours with load of
900 amp and then it goes in shutdown with alarm fault
messege of speed fault although heirtz reading fixed at
50,what does that mean
Answer / k.prakashchandra
Gen voltage can not be 550 KV which I think ,is the tr
voltage. Hz is at 50 even after gen has tripped.That
means ,it was connected to grid.The gen might have tripped
on over speed due to load throw-off. If not, speed sensor
of the gen is to be checked
| Is This Answer Correct ? | 0 Yes | 0 No |
List the materials required for Pipe Earthing.
how was your last weekend.
why they charge more bill for low power factor rather than high power factor
Hi My Dear All Friends, There is one question it is widely used in Power Project's High Voltage Engineering. Question- What is the diffrence between Earth fault and Back up Earth Fault....???? . . . . . . Have A Good Day
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
what is called star connection and delta connection also purpose of this connections?
how to select energy meter? have any calculation?
How to decide and select the different earthing wire size for the different types of earthing
How to prepare electrical preventive maintenance plan & shedule of machine tools in manufacturing unit.
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
How can we calculate the Rating of DG Set for a 4 kw motor?
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)