how will protect transformer agint overcurrent protection
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
Full load current, we can see on name plate of the
Transformer. use the correct rating for fuse according to
full load current. If load is more than 2 mega watt then we
can use a air or vacuum type circuit breaker.
Is This Answer Correct ? | 16 Yes | 4 No |
Answer / silpa
hi shaik, over current relay is only to sence the fault,
circuit breaker's role is to protect
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / aravind
A Differential relay can be used to detect transformer over
current.The Earth fault relay can be used to detuct over
current thro' earth.(These relays ultimately going to
initiate the circuit breaker to interupt the fault)
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / manish mishra
i agree with silpa..relay is used only for sensing but the
interruption is performed by circuit breaker...so by using
OC breaker we can protect the transformer from the OC...
Is This Answer Correct ? | 2 Yes | 5 No |
what is the role of reactive powerin transmission and distribution?
could anybody able 2 send me jindal steels previous papers fr electrical steam....pls send 2 my id if possible....sirisha.shaik@gmail.com
how to select fuse in any circuit? if with fomula ?and examples also
wat is d diffr btw shunt coil and trip coil in VCB?
what is differance bw ELCB and MCB. ?
how do we know the LT or HT panel trip by some broblem which indication willshow
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
0 Answers Alka Electromech, Aramco,
what is conductor copnstant of ab cable
what is the radio of kva & kvar or why calculated kva & kvar
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
Can the Neutral and Body Earthpits of a transformer conncted together by Earth strips under ground.