can we use a control valve without positioner

Answers were Sorted based on User's Feedback



can we use a control valve without positioner..

Answer / sbt, gmm, ypp

YES, ABSOLUTELYU. WE CAN USE CONTROL VALVE W/O POSSITIONER.
BASICALLY POSSITIONER IS USED FOR QUICK OPERATION OF
CONTROL VALVE. FOR AN EXAMPLE: IF CONTROL VALVE OPERATING
RANGE IS 0.6 TO 2.6 KG/CM2, AT THAT TIME POSSIOTIONER IS
USED FOR AMPLIFICATION FOR THE HIGH PRESSURE CONTROL VALVE
EVEN IF INPUT PRESSURE IS 0.2 TO 1.0 KG/CM2.

ANS. GIVEN BY: SBT, GMM, YPP (NFIL STAFF)

Is This Answer Correct ?    32 Yes 6 No

can we use a control valve without positioner..

Answer / baban

Yes we can use a control valve without positioner.

We can use electro-pneumatic transducer.The transducer
receives a direct current input signal and uses a torque
motor, nozzle-flapper,and pneumatic relay to convert the
electric signal to a proportional pneumatic output signal.

Is This Answer Correct ?    37 Yes 16 No

can we use a control valve without positioner..

Answer / sudalai muthusamy

Control valve can not be without positioner. The purpose of
the positioner is to control the control valve stroke so as
to keep the valve in desired position. The positioner
receives signal from the controller, and send the boosted
signal to the actuator to reach the desired position as and
when the valve reaches the desired position the positioner
cuts the boosted signal to the actuator and keeps the
position.

Is This Answer Correct ?    45 Yes 27 No

can we use a control valve without positioner..

Answer / harsh zala

Yes, We can use control valve without a positioner. The
basic purpose of positioner is to supply required punemetic
air w.r.t 4-20 mA standard signal, you can say for example
3.2 kg/cm2 to 4 kg/cm2. and it also checks for the
appropriate vavle opening(feedback) and stops air supply
going to valve actuator.

Without Positiner we can use control valve,but we must have
i/p converter, which generally converts 4-20 mA signal to
0.2 -1 kg/cm2, so in that case valve will not opearate
fully . but it will opearate upto certain level.

So when positoner got fail and we dont have new one, and if
we require valve to be controlled upto certain level, we
can use i/p converter,

Is This Answer Correct ?    20 Yes 6 No

can we use a control valve without positioner..

Answer / santosh nanavati

Yes, it can be used without positioner with the following
condition.

(1) Spring operating range should be 0.2 to 1.0 Kg/Cm2.
(2) If the application of the control valve for the
relevant process parameter control is not critical, the
valve can work without positioner i.e. it will give less
accurate output & control of parameter.

Is This Answer Correct ?    15 Yes 4 No

can we use a control valve without positioner..

Answer / m.v.ramesh

There are yes and no answers of this query.
correct answer is Yes. Most of the answers are Yes but
Explanation is a bit not clear. Yes offcource valve
positioner has lot of usages and advantages in controling
the valve position.

Answer no 8 is some what clear.
Here is the straight right answer.

"Yes we can use a control valve with out positioner when
bench set of the control valve is matching with the
standard bench set of the valves." ie, valve spring range
is 0.2 kg - 1 kg. where the process fluid is clean, and for
the valve sizes below 1 inch usually.
Where these valves need regular preventive maintanence
(lubricating and changing the packings promptly or else
these valse will give erratic positions).

Is This Answer Correct ?    15 Yes 5 No

can we use a control valve without positioner..

Answer / kuntal nayek

Yes we can use control valves without positioner.

But it will be risky as we would not able to know the
feedback that valve is working properly or not.
Normally position feedback is used to get the actual
position of the valves it is not used to control the valves.
To control a control valves we needed the process value that
usually called PV..that may be pressure, flow etc which we
could get from the transmitters or any other instruments.
According to PV controller generate corrected signal (ie.
Setpoint - Process value = error)in terms of 4-20mA.

Is This Answer Correct ?    3 Yes 0 No

can we use a control valve without positioner..

Answer / ahmed rashed

yes you can as evry body said the control valve with out
positinor can use as on/off controller

and this the apllication to use valve with positinor:
1-split range cntrol action.
2-reverse acting actuator.
3-valve size large than 3"(8cm)
4-actuator power requirment in excess of controller out put.
5-valve design inhrent of flow chractristics change.
6-line pressure above 20bar or delta pressure more than 14
bar
7-quick response actuator.
8-elminated the hystersis.
while the valve without positinor the stem fraction can
cause a control valve to exhibit hystersis

Is This Answer Correct ?    2 Yes 1 No

can we use a control valve without positioner..

Answer / vbp

Yes We Can Use The Control Valve Without Positioner But only
for the range between 0.2 to 1 kg.but it must have the I to
P for it.

Is This Answer Correct ?    2 Yes 1 No

can we use a control valve without positioner..

Answer / warren holden

Yes, a control valve can be used without a positioner.
Some of the previous responses contain correct information
about certain elements of what a positioner actually does
however they do not address the fundamental issue from a
control perspective.
The positioner on control valve is essentially a cascade
(inner) loop acting as a high gain proportional controller
within the external (outer or master) loop (Shinskey, G.F.
1988). The positioner will be beneficial if its response
time constant is faster than the master loop element(s)
i.e. in the case of a temperature control (master) loop the
control valve positioner dynamics will undoubtedly be
faster than the temperature measurement change dynamics
(this being a fundamental requirement of cascade control).
However, the control valve positioner is of no use, and
actually a hindrance, on fast acting master loops i.e. flow
control with fast change dynamics. Hence control valve
positioners are often not used on flow control loops where
the outer (master) loop flow measurement and associated
controller can handle the control valve positioning quite
well themselves.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Explain , how timer based pneumatic control valve will work ?

1 Answers  


what is the operation philosophy of proximity velocity sensor

1 Answers  


on interface level transmitter model(RTG3302-EMERSON) What is threshold valve how can we select correct threshold value T1,T2,T3,T4 When interface water & hydro carbon

0 Answers  


What is the purpose of bypass valve across AS valve.

0 Answers   ADMA OPCO,


what pressure transmitter?

8 Answers   Bhel,






What is the Difference between E/P Positioner and I/P positioner in a control valve? In which applications the respective positioners are used in?

18 Answers   ADCO,


waht is difference between pressure transmitter and transuducer

4 Answers   Gasco,


Explain the difference between the types of input variables plc?

1 Answers  


hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection

2 Answers   KCP Cements,


How to calibration of vibration probe

1 Answers   Mina Al Ahmadi Refinery,


the whole paper was based on Transducers..questions like define repeatability, error,accuracy,precision..den there were many q. on the conversion of Pa to mmHg and other units.. also..der wer few Q. on some level sensors(with diagram)

0 Answers   GNFC,


how to make a calliberation for deffirential pressure

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)