Answer / jazz
the glycol serves as a calibrating fluid for your high and
low pressure impulse tubing of the dp transmitter. In this
way since glycol has a high boiling point and does not
evaporate easily, the calibration of your dp transmitter
remains the same as long as the level of glycol (the wet leg
compensating fluid)does not change. this serves also to
protect your transmitter's electronics from high temperature
since heat will be dissipated along the way on the impulse
tubing before reaching your transmitter..
| Is This Answer Correct ? | 32 Yes | 1 No |
Answer / mohammad iftikhar
Seal pots (sometime called condensate pots) are used
to allow a liquid seal between the instrument and flowing
gases such as steam. Their function is to keep the
liquid level constant in the impulse tubes. For example,
in boiler liquid level applications the high pressure (HP)
side of a differential pressure transmitter is connected
to the vapor space on top of the steam drum. Steam
condenses in the chamber or seal pot and fills the impuls
eline with condensate. The seal pot is located to
allow the condensate to drain back to the source thus
keeping the liquid level constant.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / christian
it serve as protection to the instrument.it contain glycerin
or water vapor.with the principles of pascals law.external
pressure will be undiminished.
| Is This Answer Correct ? | 6 Yes | 3 No |
if some meteriel come in impulse line he will block the
impulse line same like caustic sulphar thats why we fill
the glycol and also trasmiter superation and wet leg
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / suresh
The main purpose of filling Glycol is
(1) to avoid depositing of liquid with high density from the process which causes erratic reading. Glycol is having a density of more than 1.1 and normally liquids with less than this value will never settle down in the impulse line, giving a constant head which is suppressed or elevated to zero during the calibration.
(2)To transmit signals from process to transmitter where high viscous or solidifying products at ambient temperature is to be measured.Steam tracing can be avoided.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dsyedjaffer
Glycol used to portect electrions compounts ofthe transimeter.incase process variable is low density &pressure ie:white petrol
is easily evapourte inthe impulse line so we are used it.it is withstand high tem(1000 degree) so it used steam line
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / murali
it isolated the mix up of high pressure tapping & process
line fluid.and if any vapour presented in HP tapping fluid
it will remove it
| Is This Answer Correct ? | 0 Yes | 9 No |
what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason
19 Answers Ecoboard, Jindal, Sepco,
in current transmitter why we use 4-20ma ???
(1) In turbine, what does term CDP, NI, NH, HSSOC, means. (2) What is the purpose of LO overhead tank in turbines.(3) An equipment is certified for EEX, IA, IIC,T6, what do you under stand by this.(4) what is SURGE, and how it is prevented, what is the purpose of bypass valve across AS valve.(5) Give 2 application of quartz crystal used for process parameter measurement.(6) what is meant by cold float of compressor shaft. (7) state four different types of flow measurement. For gas flow measurement mmscfd is the common unit. Expand the unit and specify significance of word S in the unit.(8) what is meant by Gap voltage, in vibration measurement. Normally how much Gap voltage is set and state the reason.(9) what will the new flow factor if D/P transmitter is Re-Ranged from 25” wc to 50” wc.(10) what is the usage of QDV & Volume booster.
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
what is the difference between hub and switch?
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
how u calculate ai/di/ao/do capacity in ur dcs?
Can anybody tell me the exact explanation for Functional calibration?When it should be done on process or on lab? Advanced Thanks
why two probes are used in turbine flowmeters?
What is the difference between rich gas and lean gas?
how can i communicate with non-national instruments device with pc via labVIEW8.2
3 Answers Google, Mico, National Instruments,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)