can we use a control valve without positioner
Answers were Sorted based on User's Feedback
Answer / ashish namdev
YES
1. put air pressure at a certain value (according max air requirement for actuator full action )
2. then connect limit switch at several position (0-100 scale)
3. then make a logic for open & close control action with use limit switch feedback.
4. connect air inlet with solenoid or pilot valve.
Ashish Namdev (Sr. Engg)
Jaypee Power Plant,
Bina (MP)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kamesh.g
No we can not control the control valve without positioner
eccept on-off type control valves ,Positioner main purpose
is boostup the air signal from I/P and put the position as
per your requirement ( Command)positioner link rod will
give the feedback to control valve air command air supply
so it can adjust the valve in correct position.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / m.ra
Yes we can operate a control without a positioner in the
following condiotions.
1) Volume booster is not required.
2) Operation of control valve will be very sluggish.
3) Charecteristics of control valve cannot be changed.
4) If the valve is self regulation than also positioner is
not required.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / ajith294
here more answers reagrading positioner
maximum of the answers are 'YES' especially Answer number
10,
then i have a doubt that how control a valve at 50% open,
with out a positioner.
if there is not a positioner, how we can control the valve
( control the pnumatic pressure is applied the
actuator)?????
if a valve it using fully open of fully close condtion
throgh Solenoid Valve ( bypass the air to actuator) is on
off valve.
Without a positioner we cannot control the valve through a
controller.
thanks
| Is This Answer Correct ? | 1 Yes | 6 No |
Answer / sandy
The name itself indicates the function of the positioner. A
control valve without positioner will act as a ON-OFF valve.
| Is This Answer Correct ? | 13 Yes | 21 No |
Answer / yogesh
On-off control valve can use without positioner. but globe
control valve can not use without positioner.
| Is This Answer Correct ? | 6 Yes | 24 No |
The Design Calculation of Level Transmitter For Different Structure open & Closed Vessel, Eg. Diff. Level Tx., Capacitance For Continous Operation
what is Analog input/output & Digital input/output,
2 Answers Bapco Bahrain Petroleum Company,
control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also good condition & incoming inst air line also constant pr.kindly give us correct answer?
What properties or parameters to be taken into consideration for protection while selection of Dcs controller.
wht is dcs architecture ? can u give example?
What is the difference between Error and Offset.
Which of the following instruments consumes maximum power during measurement?
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i
what is flow equation of kg/hr to m3/hr
Please any one can provide latest aptitude test,technical test and interview questions for tata consulting engineering (TCE) i need it asap thanks in advance
How to work & calculated output of the Derivative action in pid controller (Explain Derivative controller)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)