Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to Calibrate variable Head flowmeter (Orifice), here we
dont know High pressure and low pressure then how to apply
pressure on HP and LP side ?



How to Calibrate variable Head flowmeter (Orifice), here we dont know High pressure and low pressu..

Answer / carl_ellis

The situation must be an installed, running system, with a receiver that displays a flow rate from the DP pressure signal, because no one just has a DP transmitter across an orifice plate for fun.

Every differential pressure primary flow element is assumed to be zero flow at zero DP. So the DP low side pressure 'zero' will always be zero DP, or when the 3 valve manifold has its process connection valves closed and the equalizing valve open.

The measured DP represents some flow rate on the square rooted curve of the normalized percentage of span.

In order to determine the DP span value, you measure the actual DP and note what the flow rate reads on the receiver (PLC/DCS/recorder/indicator/controller) at that DP.
Then you can calculate what the DP span value is for the max flow rate that receiver is configured for.

The receiver has some configured flow range: 0-500gpm? 0-1,000 bpd? 0-650pm? Find out what it is.

For example, say you measure a DP value of 700mm wc and that 700 mm wc shows a flow rate reading of 264.5 lpm on the receiver.

You have discovered that the receiver is scaled 0-500 lpm for that DP transmitter and the receiver does the square root extraction.

What is the flow rate as percentage of flow span?
264.5 lpm/500 lpm = 52.9% of flow rate span

52.9% normalized is 0.529

Since the flow rate is the square root of the normalized DP span, you need to square the normalized percentage of flow rate to find the equivalent percentage of DP span.

0.529^2 = 0.2798, or 27.98% (~ 28%) of the DP span.
If 700mm is 28% of span, 100% of span is 2500mm wc.

So the DP span for the transmitter is 0 (no flow) to 2500mm wc (max flow).

Carl Ellis
Measure First

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

WHY WE WILL USE 0-24VdC IN ELECTRONIC CIRCUITS AND INSTRUMENTATION TRANSMITTERS?

3 Answers   Aban Power, Jindal, JSW, Sugar Factory,


what is meant by calibration

3 Answers  


What is the out put of pressure switch & electronic pressure transmitter.

5 Answers   ADMA OPCO, Al-Barrak,


what is purpose of three way manifold valve using for dp transmitter

1 Answers  


what is dead weight tester and where it is used?.

11 Answers   DuPont, Jain steels,


explain Cascade Control strategy with the help of a block diagram. also exlain its working in a distillation column

2 Answers   ABB, Sabic,


How can I map a tank?  Tank 15m h and 42m dia. we just fixed radar type lit. its reading shows over range. Now its required mapping ?

1 Answers   CMC,


a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?

1 Answers  


When can a bypass not used on a positioner?

1 Answers   CCIE,


what is field bus system. need defination

3 Answers   Takreer,


What is the constant voltage unit?

0 Answers  


Which is your favourite subject & explain any one topic of it.

0 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)