Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to Calibrate variable Head flowmeter (Orifice), here we
dont know High pressure and low pressure then how to apply
pressure on HP and LP side ?



How to Calibrate variable Head flowmeter (Orifice), here we dont know High pressure and low pressu..

Answer / carl_ellis

The situation must be an installed, running system, with a receiver that displays a flow rate from the DP pressure signal, because no one just has a DP transmitter across an orifice plate for fun.

Every differential pressure primary flow element is assumed to be zero flow at zero DP. So the DP low side pressure 'zero' will always be zero DP, or when the 3 valve manifold has its process connection valves closed and the equalizing valve open.

The measured DP represents some flow rate on the square rooted curve of the normalized percentage of span.

In order to determine the DP span value, you measure the actual DP and note what the flow rate reads on the receiver (PLC/DCS/recorder/indicator/controller) at that DP.
Then you can calculate what the DP span value is for the max flow rate that receiver is configured for.

The receiver has some configured flow range: 0-500gpm? 0-1,000 bpd? 0-650pm? Find out what it is.

For example, say you measure a DP value of 700mm wc and that 700 mm wc shows a flow rate reading of 264.5 lpm on the receiver.

You have discovered that the receiver is scaled 0-500 lpm for that DP transmitter and the receiver does the square root extraction.

What is the flow rate as percentage of flow span?
264.5 lpm/500 lpm = 52.9% of flow rate span

52.9% normalized is 0.529

Since the flow rate is the square root of the normalized DP span, you need to square the normalized percentage of flow rate to find the equivalent percentage of DP span.

0.529^2 = 0.2798, or 27.98% (~ 28%) of the DP span.
If 700mm is 28% of span, 100% of span is 2500mm wc.

So the DP span for the transmitter is 0 (no flow) to 2500mm wc (max flow).

Carl Ellis
Measure First

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

whey we conect ammeter in series and voltmeter in parallel in circuit

1 Answers  


what's the criteria of using over range protector when installing Pressure Gauge

1 Answers  


1. How many output signals do wew have in process control? 2. Could you write down the names of the pre-commissioning and commissioning stage test instruments and explain them (more than 5 items)? 3. What is the first step to commission a transmitter on service? 4. What is RTD? 5. Find the output value in MA of a temperature transmitter (RTD Type) at 120degree celius? 6. What is the O/P signal of a pneumatic transmitter? 7. What is the O/P signal of an elctronic transmitter? 8. What is the close loop and open loon?

4 Answers  


How to Calibrate Ultrasonic Level Transmitter in field

0 Answers  


how we calculate the range of flow from a dp?i mean if we have a dp,3810mm h2o.how much flow ranges we can use for this DP?

1 Answers  


what is isloted barrier how it works and what are the main purpose.how it make safe area.

0 Answers  


why using negative supply for bentley nevada vibration system ?

0 Answers  


what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me

2 Answers   HCL, SOC,


why is honed type flow orifice plate? what purpose it used? how to select this?

4 Answers  


how can use ram

0 Answers  


what is the working principle of hydra step(electronic level indicator)?

2 Answers   Bengal Energy, Lanco,


My friend has faced this question! I don't know clearly. So please anyone give me the correct and short answer to this question? What is variable frequency drive? Types, what is star to delta? Why this arrangement necessary?

5 Answers   Asian Paints, TCS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)