How to Calibrate variable Head flowmeter (Orifice), here we
dont know High pressure and low pressure then how to apply
pressure on HP and LP side ?
The situation must be an installed, running system, with a receiver that displays a flow rate from the DP pressure signal, because no one just has a DP transmitter across an orifice plate for fun.
Every differential pressure primary flow element is assumed to be zero flow at zero DP. So the DP low side pressure 'zero' will always be zero DP, or when the 3 valve manifold has its process connection valves closed and the equalizing valve open.
The measured DP represents some flow rate on the square rooted curve of the normalized percentage of span.
In order to determine the DP span value, you measure the actual DP and note what the flow rate reads on the receiver (PLC/DCS/recorder/indicator/controller) at that DP.
Then you can calculate what the DP span value is for the max flow rate that receiver is configured for.
The receiver has some configured flow range: 0-500gpm? 0-1,000 bpd? 0-650pm? Find out what it is.
For example, say you measure a DP value of 700mm wc and that 700 mm wc shows a flow rate reading of 264.5 lpm on the receiver.
You have discovered that the receiver is scaled 0-500 lpm for that DP transmitter and the receiver does the square root extraction.
What is the flow rate as percentage of flow span?
264.5 lpm/500 lpm = 52.9% of flow rate span
52.9% normalized is 0.529
Since the flow rate is the square root of the normalized DP span, you need to square the normalized percentage of flow rate to find the equivalent percentage of DP span.
0.529^2 = 0.2798, or 27.98% (~ 28%) of the DP span.
If 700mm is 28% of span, 100% of span is 2500mm wc.
So the DP span for the transmitter is 0 (no flow) to 2500mm wc (max flow).
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 1 No |
what is difference between venturi and orifice
What is mean by analytical instrumentation?
what is the difference between RS 232,RS 485,RS 422, how they different from each other
What Is Pre- Commissioning Package +what is DCS & ESD Pre- Commissioning for Instruments Please explain your answer on practical ground base
Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..
in pressure gauge inside why we are using the glasarin oil?
how can we tune a PID. If it is by zeiger nichols method..please explain briefly with help of an example.
With N nodes and B branches what will have a network ???
If any control valve create hunting problem, what is the possible reason and solution?
why are use only 4 to 20ma. signal.
Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell
Questions on flow meters,few questions on HART protocol,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)