How to calculate the average power factor in 3 phase
unbalanced system
Answers were Sorted based on User's Feedback
Answer / thakur
Simply calculate total KWH and KVH of last 24 Hrs and
Divide into-Total KWH/Total KVH=Avg PF of last 24Hrs
| Is This Answer Correct ? | 34 Yes | 9 No |
Answer / engr.abdurrahim
Dear Deepak,
Power factor is the cosine factor of the voltage & current
phase difference. Its a short defination. But if you go
deeply, Power factor=cos@,its depend only on load, instead
of phasewise.if you connect same load in every phase it
will show same power factor value in each phase.Because
power factor is depended upon load resistance=R & its
impedance=Z,
cos@ = R/Z,
So if you are going to calcualte the power factor of all
phase, you have to calculate all resistance & impedance of
the load. Then you can calulate the avg. power factor.
R=R1+R2+R3
Z+Z1+Z2+Z3
(Where Z=R+jXL=Impedance)
cos@=R/Z
Hope my answer will satisfy you.
Best Regards,
Engr.Abdurrahim
shaikh337@rediffmail.com
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / razi zainal abidin
Dear all,
This is not an answer, actually question.
In one factory, we are dificult to measure resistance,R and
impedance, Z.
What we have is only voltage supply (3phase, 420volt), and
total current flow during maximum usage using clampmeter
(including machinery, lamp, computers, etc...)
We also have info of main transformer step down because it
is in the factory area. Normally they stated value of KVA.
And some factory already install the 'capasitor bank
regulator'
So, how we can calculate the CORRECT VALUE of capasitor
need to install?
I mean, which one is the correct KW, which one is the
correct KVA, and how to calculate existing power factor IF
the factory already have 'capasitor bank regulator'....can
we switsh of the regulator?
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / reddy
By using sequence components ... (+vesequence power - -ve
seq power)/VA
| Is This Answer Correct ? | 0 Yes | 4 No |
How to do the meggering for a cable.
In what situations relays are used in Circuit breaker? In Above what rating of Circuit breaker the relays are used? Why relays are not used for CB like MCB?
How to model "IF ELSE" statement in matlab simulink?
How generating electric power export to grid from the generating station ?
what are the alternator cooling system? how it is represented?
what is diffential relay? testing proceure?and transformer reach Over load thet time differencilal relay operate or not ?
in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in primary side. To obtain 700v. which tapping should be used of HV side as we have 11000v/720v tapping now .
I don't understand why when we connect high voltage source in DC to electronic motor , we must add capacitor and resistor in parallel ? (I know that we use capacitor because we want to absorb the current that in the first second electronic motor in opposed with current course produce. ) what are the feature of Resistor and in such situation ?
what is the advantage of pwm pulse compare to squarewave pulse.
What is power factof?
For 6600/433 distribution transformer we apply secondary side 433 volts how much voltage in primary side.
what is the diff. b/w restricted earth fault relay & standby earthfault relay and where they are used?
4 Answers KSK Energy, Reliance,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)