how to check the continuity of a cable with a megger
Answers were Sorted based on User's Feedback
Answer / dasharath waghmode
To check the continuity of a cable, first short any two cores of a cable at one end and test same cores for continuity on other end by megger. If both cores are open it will show high resistance and if not will show zero resistance. And repeat the same process for other cores.
Is This Answer Correct ? | 4 Yes | 0 No |
its very simple
Connect the other ends of cable togather and take megger from other end at very low voltage, if megger is zero means it is continuty is one, again seprate the the cable and take the megger if megger is more tha 100 Kohm, means cable is healthy.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / guest
we connect the megger to cable then read the megger reading. If this reading is infinity then your cable will ok. Or megger does not show infinity then your cable is cut or insulation level is decreased
Is This Answer Correct ? | 0 Yes | 0 No |
Do not check continuity with megger , use multi meter
Is This Answer Correct ? | 0 Yes | 0 No |
what is difference between KW and KVA
how to calculate kvar in Akiva
what is difference between earhing and neutral
What kind of Neutral CT can be placed in 11/0.433KV transformer to be used and what are its specification?
what is MULTIPLYING FACTOR in substations??
What do you mean by distribution transformers?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
Size of the 60Hz and 400Hz transformers is a) same b) 60Hz Tr s larger than 400Hz Tr c) 400Hz Tr s larger than 60Hz Tr d) None of the above
why 6.6,11,22,33,66kv? what basis they have considered?
What is the main feature of v/f control?
what is the pre charge circuit,what will be work which function it will be use plz tell me
HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii) DELTA LOAD, USING A CLAMP METER. NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO WE GET?? PHASE CURRENT OR LINE CURRENT.