Answer / rvg

A llose connection contact can produce following effects:

1. Spark b/w cable and equipment.
2. Damage of cable lugs.
3. Heating of any insulation nearby.
4. can ignite any inflamable material near by
5. voltage reduction b/w the terminals etc.

Is This Answer Correct ?    79 Yes 6 No

what are the affects of loose connection in electrical circuit...

Answer / tauseef tarique, engineer(e)

Loose connection is the most Dangerous thing in the
electrical enginnering and one should always avoid it.

Due to loose connection the contact resistance will
increase and when the current flows through it, it will
start heating at the connection point and if the current
continues the contact point may melt and disconnect the
supply.

Because of sparking due to loose connection the instrument
connected with this line may be damaged.

Is This Answer Correct ?    57 Yes 4 No

what are the affects of loose connection in electrical circuit...

Answer / er.s.kant.

less current and spark. on heavy load it may burnt.

Is This Answer Correct ?    41 Yes 16 No

what are the affects of loose connection in electrical circuit...

Answer / sanjeet

sparking will occur
short circuit may occur
single phasing may occur
electrecal instrument may distroy

Is This Answer Correct ?    23 Yes 4 No

what are the affects of loose connection in electrical circuit...

Answer / avd

Loose connection ==> High resistance point in circuit ==>
Hight I2R drop at that point ==> temperature rise ==>
further increase in resistance and so on. finally
flash/burn and disconnection of circuit.

Is This Answer Correct ?    18 Yes 3 No

what are the affects of loose connection in electrical circuit...

Answer / aruna devi

leakage current and spark will occur.

Is This Answer Correct ?    24 Yes 12 No

what are the affects of loose connection in electrical circuit...

Answer / kbuuka john ivan (i.j.k)

Due to the loose connection,there is an air gap between the electrical contacts which results in high contact resistance.If current continues to flow,I2R loses(heat)will increase and later lead to melting of contacts and thus causing an open circuit.
Most electrical fires are mainly caused by a lot of heat that is generated as a result of loose connections.

Is This Answer Correct ?    9 Yes 0 No

what are the affects of loose connection in electrical circuit...

Answer / john o. wee

increase resistance and increase in line current and makes
the contact point to burn and melted the insulation and can
cause fire due to overheating

Is This Answer Correct ?    13 Yes 6 No

what are the affects of loose connection in electrical circuit...

Answer / pavan

Loose connection will cause low current and sparking and
sometimes it may cuase damage to the system.

Is This Answer Correct ?    16 Yes 10 No

what are the affects of loose connection in electrical circuit...

Answer / mizanur rahman

High voltage drop in the loosely connected point due to
increased resistance, more current flow through the point &
the point is overheated, as a result, it melts the conductor

Is This Answer Correct ?    13 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of 4-pole ACB or any switchgerar..Please guide me why is it so????

4 Answers   Piramal Glass Limited,


what is the minimum distance between substation wall and LT panel outer surface?

3 Answers   L&T,


How many size of cable required for a 300m long and 30kw inductive lode

0 Answers  


What is rotor angle stability?

2 Answers  


Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb

1 Answers   CIMC,






main difference between ac and dc?

0 Answers   Classic Network,


how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???

0 Answers  


how am i achived model paper to prepratio for bhel exam

2 Answers   Bhel,


What are the RGGVY, APDRP, RE?

3 Answers  


If we have use two power cable for incomer, that time how many use cbct for earth leakage protection? 1 or 2 if 1 way? If 2 way?

0 Answers   REM Electromech Pvt Ltd,


what is difference between KW and KVA

1 Answers  


in non technical way how can u define POWER FACTOR??

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)