Answer / tauseef tarique, engineer(e)
Loose connection is the most Dangerous thing in the
electrical enginnering and one should always avoid it.
Due to loose connection the contact resistance will
increase and when the current flows through it, it will
start heating at the connection point and if the current
continues the contact point may melt and disconnect the
supply.
Because of sparking due to loose connection the instrument
connected with this line may be damaged.
| Is This Answer Correct ? | 57 Yes | 4 No |
Answer / er.s.kant.
less current and spark. on heavy load it may burnt.
| Is This Answer Correct ? | 41 Yes | 16 No |
Answer / avd
Loose connection ==> High resistance point in circuit ==>
Hight I2R drop at that point ==> temperature rise ==>
further increase in resistance and so on. finally
flash/burn and disconnection of circuit.
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / kbuuka john ivan (i.j.k)
Due to the loose connection,there is an air gap between the electrical contacts which results in high contact resistance.If current continues to flow,I2R loses(heat)will increase and later lead to melting of contacts and thus causing an open circuit.
Most electrical fires are mainly caused by a lot of heat that is generated as a result of loose connections.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / john o. wee
increase resistance and increase in line current and makes
the contact point to burn and melted the insulation and can
cause fire due to overheating
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / pavan
Loose connection will cause low current and sparking and
sometimes it may cuase damage to the system.
| Is This Answer Correct ? | 16 Yes | 10 No |
Answer / mizanur rahman
High voltage drop in the loosely connected point due to
increased resistance, more current flow through the point &
the point is overheated, as a result, it melts the conductor
| Is This Answer Correct ? | 13 Yes | 8 No |
As the one point of eac phase winding is connected to each other in satr connction. Even if that at distribution side collesion of two diff phases result in to blast. Why?
why we don't discuss power facter in dc?
how point on wave controller works.
Wtat is mean by GHOAST VOLTAGE?
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
minimum ohm for lighting minimum ohm for Earthing
WHAT ARE THE BELT HORMONICS IN AC MACHINE HOW TO REDUCE IT
What is differance betwwen Conventional MCC & Inteligent MCC?
during the period of armature reaction ,if the brush shift is not accomplish, what happen?
what is the transformer efficiency?
3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)