what are the affects of loose connection in electrical
circuit.
Answers were Sorted based on User's Feedback
Answer / tauseef tarique, engineer(e)
Loose connection is the most Dangerous thing in the
electrical enginnering and one should always avoid it.
Due to loose connection the contact resistance will
increase and when the current flows through it, it will
start heating at the connection point and if the current
continues the contact point may melt and disconnect the
supply.
Because of sparking due to loose connection the instrument
connected with this line may be damaged.
Is This Answer Correct ? | 57 Yes | 4 No |
Answer / er.s.kant.
less current and spark. on heavy load it may burnt.
Is This Answer Correct ? | 41 Yes | 16 No |
Answer / avd
Loose connection ==> High resistance point in circuit ==>
Hight I2R drop at that point ==> temperature rise ==>
further increase in resistance and so on. finally
flash/burn and disconnection of circuit.
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / kbuuka john ivan (i.j.k)
Due to the loose connection,there is an air gap between the electrical contacts which results in high contact resistance.If current continues to flow,I2R loses(heat)will increase and later lead to melting of contacts and thus causing an open circuit.
Most electrical fires are mainly caused by a lot of heat that is generated as a result of loose connections.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / john o. wee
increase resistance and increase in line current and makes
the contact point to burn and melted the insulation and can
cause fire due to overheating
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / pavan
Loose connection will cause low current and sparking and
sometimes it may cuase damage to the system.
Is This Answer Correct ? | 16 Yes | 10 No |
Answer / mizanur rahman
High voltage drop in the loosely connected point due to
increased resistance, more current flow through the point &
the point is overheated, as a result, it melts the conductor
Is This Answer Correct ? | 13 Yes | 8 No |
For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of 4-pole ACB or any switchgerar..Please guide me why is it so????
4 Answers Piramal Glass Limited,
what is the minimum distance between substation wall and LT panel outer surface?
How many size of cable required for a 300m long and 30kw inductive lode
What is rotor angle stability?
Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb
main difference between ac and dc?
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
how am i achived model paper to prepratio for bhel exam
What are the RGGVY, APDRP, RE?
If we have use two power cable for incomer, that time how many use cbct for earth leakage protection? 1 or 2 if 1 way? If 2 way?
0 Answers REM Electromech Pvt Ltd,
what is difference between KW and KVA
in non technical way how can u define POWER FACTOR??