how much load 15kva dg set can bear
Answers were Sorted based on User's Feedback
Answer / jax
Sorry in above answer I have written wrongly. It is 12 kW.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / vikas m sampath
convert the kva to kw first ie kva*pf=kw so here 15*.8,(say pf is .8)now the ans is 12kw so up to 24amps out of this generator company say u got to put in only 80percent load of 24amps so about 19amps u can load for economy
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / jax
Normally DG is rated for 0.8 pf. So DG can bear upto 15 kW.
For any doubt in electrical please contact
jaxp333@yahoo.co.in
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / tanvir
15 kva dg set can use for 25 amp 3 phase load with
calculation of power factor 0.8.
Is This Answer Correct ? | 9 Yes | 10 No |
How we can differniate the overhead lines feeded by hydro power stations & thermal power stations
I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions
different between highvoltage & lowvoltage source
why is the HT voltages are in multiples of 11KV
Form fator is the ratio of?
WHAT IS THE SETTING OF OVERLOAD RELAY AND UNDER VOLTAGE RELAY IN PERCENTAGE?
plz send me the procedure and syllabus for mseb exam
difference between the applicability of nortons and thevenin theorem
what is the purpose of reactor in electrical substations ?
Any link for Electrical objective type questions ?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
3 Answers Infotech, Vijai Electricals,