how much load 15kva dg set can bear
Answers were Sorted based on User's Feedback
Answer / jax
Sorry in above answer I have written wrongly. It is 12 kW.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / vikas m sampath
convert the kva to kw first ie kva*pf=kw so here 15*.8,(say pf is .8)now the ans is 12kw so up to 24amps out of this generator company say u got to put in only 80percent load of 24amps so about 19amps u can load for economy
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / jax
Normally DG is rated for 0.8 pf. So DG can bear upto 15 kW.
For any doubt in electrical please contact
jaxp333@yahoo.co.in
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / tanvir
15 kva dg set can use for 25 amp 3 phase load with
calculation of power factor 0.8.
| Is This Answer Correct ? | 9 Yes | 10 No |
what are the effects on an power plant and consumers if the power factor is increased or decreased?
in electrical fire which group fier Extinguisher as used
Why ground terminal is used in pot meter 10k ohms
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
what is the technical term when and alternator's prime mover fails.
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
What may be happen if neutral and earth is shorted in a substation
what is voltage, and how it makes the electron to move?
hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
i am using star-delta connections with reverse/forward direction motion of the 75hp induction motor.What should be the ratings of Main,Delta and Star contactors and why?
why we somewhere use ryb phase sequance, somewhere use uvw, and somewhere abc??
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)