if AVR fails in alternator. what will be the effect.
Answers were Sorted based on User's Feedback
Ans: From my real experience the voltage may not come to
zero, the volltage will fluctuate from one value to another
it may not constant at any time period. with this frequency
also increases drastically. due to this there is chance of
blown down of ACB fuses and coils.
Is This Answer Correct ? | 32 Yes | 8 No |
Answer / v.d.vamshinath
There wont be any excitation to the main field other than
residual magnetism which is lost drastically(within
fraction of second) if AVR failed on load.
So voltage grops and may come down to zero.
If AVR fails when there is no load on alternator, the
residual magnetism will be sufficient to build some voltage
less than the rated voltage till it exists.
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / p.raju
The AVR scheme comes into operation only when there is a
change in loading.......
we have AVR scheme to regulate the changes in voltage level
at the alternator terminals, because of change in reactive
power loading.when AVR fails it will not increase the
voltage, thats why further decrease in voltage takes
place ..... which leads to final voltage collapse of the
system.
Is This Answer Correct ? | 17 Yes | 5 No |
Answer / culla felix
when the AVR fails in the alternator there will be no device
that will control the flactuation of the output voltage the
same thing that there will be no device that will give the
voltage excitation in the field(rotor) of an alternator, only
the residual voltage will excite the field to build up more
strong fluxes, in that matter there will be no consistent
output voltage in the alternator
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / pratap k s
it depends on the alternator field excitation circuitry. In
a brushless alternator with compound excitation the
alternator produces a high voltage around 440V with the AVR
disconnected and the AVR regulates the output volatge to a
set value say 400V even if the laod varies from 0 to 100%
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satya
alternator trip at loss of exitation because it can not
biuld up exitation voltage to the field. its null meter
becomes 0 position.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / emeka spark
I agree with Amritpal Singh Sidhu. i had similar
experience of AVR failure at the site few days ago and i
provided 12volts from the battery. innitially the voltage
was a bit higher than normal but i adjusted the governor of
the DG till i got a normal voltage.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amritpal singh sidhu
If AVR fails to work, then we troubleshoot the same by
providing the 12V DC from DG set battery to the field
winding of DG set. But in that case we should take care
that normal load can be put on, because the battery can not
regulate the voltage as the AVR done.
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / s f ali
Actually when AVR damages, although the engine is running on fine RPM you will not having voltages like your required. I personally observed that engine was running on fine RPM and I was getting 14 L-N voltages.......
Is This Answer Correct ? | 0 Yes | 0 No |
What is auto reclose system in Circuit breakers??
What is the minimum IR value of HT/ LT cable? Pls post separetely!!!!!
why field winding is placed on rotor winding not on stator winding in case of synchronous machine?
two parallel conductors are carrying the current in the same direction.which of the following statements is true? (a)there is arepelling force between the conductors (b)the force increases when the distance between the conductors is increased (c)there is an attaracting force between the conductors (d)the force increases when the distance between the conductors is decreased
Why increase in current leads to increase in conductor temperature?
what is the switching substation
what are upstream faults and downstream faults in power system
wat is power factor
In 3 phase induction motor even with low Voltage it reaches nearly it's rated speed why? (for example instead of 400V it reaches with 250V)
What is an infinite bus bar?
what r the advantage of selecting micro controller type tripping of circuit breaker than relay type tripping?
why use delta star x-mer in distribution system.