If the neutral wire go pass through the core balance current
transformer? If yes then why? and no then why?
Answers were Sorted based on User's Feedback
The neutral is requiered to pass through the core balance
CT together with the phase for the same circuit. It
operates on the current going through the pahse being
balanced with the current returning through the neutral. If
these are balanced the protection will not operate. If a
fault occurs (a short circuit to earth in either the phase
or neutral)some current will flow through the earth to the
neutral and not go through the CBCT. This will then operate
the protection.
| Is This Answer Correct ? | 6 Yes | 1 No |
If Current Flowing through the cable is balanced then
output of the CBCT through which the cable is passing is
zero. If you pass the Neutral through the CBCT and if fault
occurs then part of fault current will flow through the
Neutral which will also travel through the CBCT and CBCT
will not produce any output hence Protection will not
operate. Hence Neutral should not be passed through the CBCT
| Is This Answer Correct ? | 3 Yes | 4 No |
what is O.T?specify the acceptable range?
how to calculate neutrel current
We have 2 11kv/433v transformers for 2saperate acb for mv panels and 1 bus coupler acb. Suppose I’ll close bus coupler what will happen or it will be share the load. Please suggestion and any modification required.
where any change in supply line due to the incipient faults in three phase induction motor
What is magneto on a gas generator. how it functions. its out put is d.c or a.c. how it can be checked for correct functioning
What is phase cross over frequency?
why near the transformers, the Jelly(small white colored rocks)are poured.and what are conditions for that?
WHAT IS M.P.C.B
Why using synchronising methed in DG's sets?
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
0 Answers Eprosys Engineering Consultants,
What is the reasonable voltage between Neutral & Earth of an electrical system for good earthing?
Brushes are placed at magnetically neutral axis,when brushes reach that point,the armature conductor gets shorted,but it can be seen that the dc supply is also shorted,wont that get damage? help me plz
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)