if 20 hp motor starts directly stars and contenious run .
what will be the effect.
Answers were Sorted based on User's Feedback
Answer / nishant
For staring of Motor above 5 HP we need a starter with
overload protection e.g. Star-Delta Starter and D.O.L.
Starter for limiting starting current as motor takes 5-7
times of its full load current during starting So if we
start 20 HP motor Directly the line fuses will Blown Off
due to high starting current.
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / sdr
Dear readers, you may please note that Induction motor of
any size can be started directly-on-line provided that the
system in which it is connected should be healthy enough to
keep the system voltage steady at the time of starting.It
is not at all deirable to use a starter if your system is
healthy.In practice ,we usally don't know how much our
system is loaded,so be at a safer side, we use starters to
start Inductin motors.Thus starters limit the high inrush
current at starting & keep the system voltage almost steady
to let peform the other machines steadily.
If a 20 HP motor started in star & kept continuosly running
in star, it will run but the capacity of motor will reduced
to 57.73percet of the rated one.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mallikarjuna
Dear all readers so that if we 20hp motor start directly in
star nothing will happen and starting current will
less,suppose if connect to the motor in DOL starter the
starting current is 5-6 times full load the starting
current is around 150 amps ,when we connect to the star the
starting current is 60amps
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / ramya
above 10 hp we required starter bcoz, during the starting
of the motor ll get damage due to over starting current,
over voltage, increase in winding temparature,
thus to controll those faults we need decrease in starting
current, thus we run the motor with the starter. the name
itself indicates that it is uesd to start the drive or
motor.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / hari
DIRECT STARTING WITHOUT STARTER IS POSSIBLE FOR DOL type
windings only,not for double cable motors.sudden load will
effects the transfomer and other electricl accessories.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / dharmesh doshi
motor have no any problem to run but power consumption is high due to low power factor.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / umesh
whenever we starts the 20hp motor directly with the mains
then its winding will be burnt, because the motor winding
have less then 10ohms, whenever current flows though the
winding the current will be 5000A, then it will be burnt.
that's way we use the starters for safty.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / brijesh soni
If the motor strrted ok but if any Problem during at the
running as single phasing, over lodin, the motor will be
never Trippd but it will be Burn out
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / amit kumar
In this case , it delivers only one third power of the
rated capacity of the motor.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / er.nitesh
Nishant is right but i want to say above 5 HP we use Star
delta starters and below it we use D.O.L.
| Is This Answer Correct ? | 0 Yes | 5 No |
How power factor affect on bill explain with example.
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
what is defference by mcb,mccb and mpcb
WHAT IS NORMAL VECTOR GROUP USED FOR DESIGNING OF TRANSFORMERS??
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
how to convert kw in to unit
Is 2000kva stabilizer suitable for 1h.p split air conditional
what is the voltage regulation for unity and zero power factor?
In 2500kva transformer how much is the withstand High voltage power frequency between primary to secondary and earth? And secondary to primary and earth?
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
Can CT Secondary left open circuited and why(reason)?
what principle the cabel TV channels are transmitted? will you be able to check the power at the connector behind your TV with a tester?If yes what is the supply level?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)