if 20 hp motor starts directly stars and contenious run .
what will be the effect.
Answers were Sorted based on User's Feedback
Answer / nishant
For staring of Motor above 5 HP we need a starter with
overload protection e.g. Star-Delta Starter and D.O.L.
Starter for limiting starting current as motor takes 5-7
times of its full load current during starting So if we
start 20 HP motor Directly the line fuses will Blown Off
due to high starting current.
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / sdr
Dear readers, you may please note that Induction motor of
any size can be started directly-on-line provided that the
system in which it is connected should be healthy enough to
keep the system voltage steady at the time of starting.It
is not at all deirable to use a starter if your system is
healthy.In practice ,we usally don't know how much our
system is loaded,so be at a safer side, we use starters to
start Inductin motors.Thus starters limit the high inrush
current at starting & keep the system voltage almost steady
to let peform the other machines steadily.
If a 20 HP motor started in star & kept continuosly running
in star, it will run but the capacity of motor will reduced
to 57.73percet of the rated one.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mallikarjuna
Dear all readers so that if we 20hp motor start directly in
star nothing will happen and starting current will
less,suppose if connect to the motor in DOL starter the
starting current is 5-6 times full load the starting
current is around 150 amps ,when we connect to the star the
starting current is 60amps
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / ramya
above 10 hp we required starter bcoz, during the starting
of the motor ll get damage due to over starting current,
over voltage, increase in winding temparature,
thus to controll those faults we need decrease in starting
current, thus we run the motor with the starter. the name
itself indicates that it is uesd to start the drive or
motor.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / hari
DIRECT STARTING WITHOUT STARTER IS POSSIBLE FOR DOL type
windings only,not for double cable motors.sudden load will
effects the transfomer and other electricl accessories.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / dharmesh doshi
motor have no any problem to run but power consumption is high due to low power factor.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / umesh
whenever we starts the 20hp motor directly with the mains
then its winding will be burnt, because the motor winding
have less then 10ohms, whenever current flows though the
winding the current will be 5000A, then it will be burnt.
that's way we use the starters for safty.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / brijesh soni
If the motor strrted ok but if any Problem during at the
running as single phasing, over lodin, the motor will be
never Trippd but it will be Burn out
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / amit kumar
In this case , it delivers only one third power of the
rated capacity of the motor.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / er.nitesh
Nishant is right but i want to say above 5 HP we use Star
delta starters and below it we use D.O.L.
| Is This Answer Correct ? | 0 Yes | 5 No |
Why the CT Secondary is rated as 5A generally?
How frequency meter measuring frequency? What is the principle of frequency meter?
I have finish diploma electronics and five years experience in electrical field in ht service how can i get c licensce or other electrical certificate
Are same transformer be employed for step up and step down services?
what will happen if a part of primary winding of a transformer is accidentally short-circuited?
If NO contact of relay gets supply from other sources or other part of circuit and at a time relay coil activates,then current will flow in which direction & will it cause to damage relay??
How we calculate the size of ht cable for any transformer
Why the capacitor bank is keeping on for electricity supply and keeping it off for generator supply
How earth fault & earth leakage equvpment are works?
what is the different between RCCB & ELCB
What is spike & surge.
how the direction of rotation in a dc shunt motor could be reversed?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)