if 20 hp motor starts directly stars and contenious run .
what will be the effect.
Answer Posted / sdr
Dear readers, you may please note that Induction motor of
any size can be started directly-on-line provided that the
system in which it is connected should be healthy enough to
keep the system voltage steady at the time of starting.It
is not at all deirable to use a starter if your system is
healthy.In practice ,we usally don't know how much our
system is loaded,so be at a safer side, we use starters to
start Inductin motors.Thus starters limit the high inrush
current at starting & keep the system voltage almost steady
to let peform the other machines steadily.
If a 20 HP motor started in star & kept continuosly running
in star, it will run but the capacity of motor will reduced
to 57.73percet of the rated one.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
draw the block diagram of fire alarm?
what are different types of electrical windings? i know the distributed winding ,concentrated winding etc but i want some detailed information, in what condition we will use distributed,concentrated windings what are the difference between them which is best, how induced emf changes by using different types of windings 20 hours ago - 1 week left to answer
how to synchronize 3 phase slip ring induction motors of different ratings.
how to select the no. of brushes in a lap winding?
help me with the question that might be ask on the interview for technical position
What is VCB? where it is installed at SP. What is SP?
What are the electrical engineer roles and responsibilities in chemical plant?
What test must you do before powering up a circuit that you have been working on?
What are the types of windings present in the ceiling fan? What winding will be effective first when we started the fan?What are the resistance and inductance ratios comparatively at the initial speed and full speed of the fan?
Can you explain about TEE protection scheme?
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
what is the interrelation between voltage current torgue speed and magnetic flux in case of different types of electric motors
what is difference between speed mode and torque mode in motor?? explain in simple words please.
What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.
what is the id1 & id2 setting in differential protection relay of CSPC?