Where the ON LOAD TAP CHANGER is provided in the setp up
transformer?
Answers were Sorted based on User's Feedback
Answer / anand yadav
In most cases, on load tap changer is provided at higher
voltage & lower current side.It is economical.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / a.muthukumar
Always ON LOAD TAP changer is provied in HV side only.
Because HV side current is low and LV side current is high.
So, during on load tap changing losses will be reduced when
on load tap changer is in HV side.
| Is This Answer Correct ? | 8 Yes | 0 No |
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
EXPLAIN METOD OF IMAGE OF TRANSMISSION LINE/ WHAT ARE ITS PRACTICAL APPLICATION?
if a single phase 3 hp submersible pump of Crompton Greaves is moving in reverse direction and sometimes it moves in rigth direction ,then what may be the cause....
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
Is it required to use Automatic transfer Switch in L&T panel board if we use AMF panel with DG set? How the single line diagram will be? Please forward the material to sreenu_207@yahoo.co.in
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
what will happen if secondary of potential transformer (220kv/110volt) of any metering core or protection core (cables) of any phase got earthed??
what is the significance of per unit impedance ?
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
I have AC automatic voltage regulator 15KVA What output currant?
DG cranking voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)