what is the difference between the HT Cable and LT Cable ?
Answers were Sorted based on User's Feedback
Answer / bkmutha
If insulation grade is 1.1 kv then we called it LT cable
and above it i.e. 3.3 kv , 11 kv we called as HT cable.
in short we can say that main difference is insulation or
property of insulation to withstand voltage stress.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / jacobdaniel
HT Cable:- 1) Its design having 4 to 5 layer of protection
to withstand the high tension voltage and also we can avoid
Voltage drop because of sensitive protection.
2)Bundle Conductor of HT Cable thickness is high than LT cable
3)HT Cable having R,Y & B Terminals without Neutral
LT Cable:- 1)Its design having 2 to 3 layer of Protection to
withstand the Low Tension Voltage.
2)LT Cable having R,Y & B Terminals with Neutral
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / ankit jain
In general we only use two words ie. LT & HT cable.
LT = below 500V
HT=Above 500V
But as per IS standard:
there are following voltage grades.
below 1000 V = LV
1100 V < MV < 36 KV
66 KV < HV < 150 KV
150 KV < EHV < 525 KV
We generally use PVC insulation for LV And MV cables. But it
is not compulsary to use PVC Cables as now XLPE cables are
more preffered because of certain advantages over PVC
Insulation.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / maneesh kumar
HT cable made in high voltage and LT cable made in high
current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / selvakrishna.s
HT Cable:- 1) Its design having 4 to 5 layer of protection
to withstand the high tension voltage and also we can avoid
Voltage drop because of sensitive protection.
2)Bundle Conductor of HT Cable thickness is high than LT cable
3)HT Cable having R,Y & B Terminals without Neutral
LT Cable:- 1)Its design having 2 to 3 layer of Protection to
withstand the Low Tension Voltage.
2)LT Cable having R,Y & B Terminals with Neutral
| Is This Answer Correct ? | 7 Yes | 5 No |
In HT cable the insulation grade is much more higher then LT
cable.
Lt cable can maximum withstand 1.1kv but whereas Ht cable
can withstand much more.
Lt cable can come with 'N',but there is no 'N' in Ht.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / a k sigh
HT cable is used for 1KV to 11KV voltage rating whereas LT cable is used upto 1KV. The basic difference in their insulation level/thichness, it is higher in HT cable LT cable.
| Is This Answer Correct ? | 3 Yes | 1 No |
For LT cable
1. Use : Up to 690V
2. Insulation : PVC
3. Core(Neutral) : Yes
4. Insulation Grading : 1100 V
For HT cable
1. Use : Above 690
2. Insulation : XLPE
3. Core(Neutral) : No
4. Insulation Grading : Above 3.3kV, 11KV..etc
( Please note that now 690 V using in VFD application with
LV cable and 440 V for DOT motor starter)
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sandeep thakur
In HT cable there is only three phase and one messanger wire,and its collects neutral from where the supply is come.
where in LT cable there is three phase,one neutral and one wire is for street light.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kishan dewangan
Both are approximate same, the only main differences
between them that is insulation.Insulation level will be
high of HT cable because it will be sustand high voltage.
| Is This Answer Correct ? | 2 Yes | 1 No |
which connection is safer series or parallel?usually which connection we prefer at home?
What will be MF if we have CT ratio is 130 of 3 nos?
which motor have relatively high power factor and what is reason for have high pf? 1.capacitor run motor 2.shaded pole motor 3.capacitor start motor 4.split phase motor
How do we calculate transformer oil in liter from the rating of the transformer.
what happen if transformer neutral not earth
Define the three phase formula fuse.
y we are used signal conditioner in capacitive transducer
What is ELR, and where it is used ?
why the India electrical supply transmission loss is high when compare to us
how will you find out the fuse failure by remote operation?
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
through which medium return supply given to alternator please answer in details
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)