Answer / bkmutha
If insulation grade is 1.1 kv then we called it LT cable
and above it i.e. 3.3 kv , 11 kv we called as HT cable.
in short we can say that main difference is insulation or
property of insulation to withstand voltage stress.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / jacobdaniel
HT Cable:- 1) Its design having 4 to 5 layer of protection
to withstand the high tension voltage and also we can avoid
Voltage drop because of sensitive protection.
2)Bundle Conductor of HT Cable thickness is high than LT cable
3)HT Cable having R,Y & B Terminals without Neutral
LT Cable:- 1)Its design having 2 to 3 layer of Protection to
withstand the Low Tension Voltage.
2)LT Cable having R,Y & B Terminals with Neutral
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / ankit jain
In general we only use two words ie. LT & HT cable.
LT = below 500V
HT=Above 500V
But as per IS standard:
there are following voltage grades.
below 1000 V = LV
1100 V < MV < 36 KV
66 KV < HV < 150 KV
150 KV < EHV < 525 KV
We generally use PVC insulation for LV And MV cables. But it
is not compulsary to use PVC Cables as now XLPE cables are
more preffered because of certain advantages over PVC
Insulation.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / maneesh kumar
HT cable made in high voltage and LT cable made in high
current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / selvakrishna.s
HT Cable:- 1) Its design having 4 to 5 layer of protection
to withstand the high tension voltage and also we can avoid
Voltage drop because of sensitive protection.
2)Bundle Conductor of HT Cable thickness is high than LT cable
3)HT Cable having R,Y & B Terminals without Neutral
LT Cable:- 1)Its design having 2 to 3 layer of Protection to
withstand the Low Tension Voltage.
2)LT Cable having R,Y & B Terminals with Neutral
| Is This Answer Correct ? | 7 Yes | 5 No |
In HT cable the insulation grade is much more higher then LT
cable.
Lt cable can maximum withstand 1.1kv but whereas Ht cable
can withstand much more.
Lt cable can come with 'N',but there is no 'N' in Ht.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / a k sigh
HT cable is used for 1KV to 11KV voltage rating whereas LT cable is used upto 1KV. The basic difference in their insulation level/thichness, it is higher in HT cable LT cable.
| Is This Answer Correct ? | 3 Yes | 1 No |
For LT cable
1. Use : Up to 690V
2. Insulation : PVC
3. Core(Neutral) : Yes
4. Insulation Grading : 1100 V
For HT cable
1. Use : Above 690
2. Insulation : XLPE
3. Core(Neutral) : No
4. Insulation Grading : Above 3.3kV, 11KV..etc
( Please note that now 690 V using in VFD application with
LV cable and 440 V for DOT motor starter)
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sandeep thakur
In HT cable there is only three phase and one messanger wire,and its collects neutral from where the supply is come.
where in LT cable there is three phase,one neutral and one wire is for street light.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kishan dewangan
Both are approximate same, the only main differences
between them that is insulation.Insulation level will be
high of HT cable because it will be sustand high voltage.
| Is This Answer Correct ? | 2 Yes | 1 No |
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts same result on 24Volts and with ground 12Volts only expert answer that thanks we can not ground the battery.
what is the purpose of %impedance for transformer
What does ampere turns shows?
How to make vector group test of transformer?
what is V0/V rating of cable
Why all transmission lines are AC, not DC line?
For a stable system, where should the poles of a system be in a root loci plot?
1.why ACB is not connected in HT side what Happens? 2.how much voltage maintained in ACB breaker? 3.OLTC is connected in primary side in case secondary side connected what happened?
what are lightning masts?what is their purpose???
what is Bucholtz Relay test???? Explain??
Why more sound is produced in mixer than grinder
Is there any problem ,if R-Y-B voltage is constant , but the air compressor taking one phase high current.what is possible causes.the said compressor is very new.(55kw).
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)