what is the difference between the HT Cable and LT Cable ?
Answer Posted / bkmutha
If insulation grade is 1.1 kv then we called it LT cable
and above it i.e. 3.3 kv , 11 kv we called as HT cable.
in short we can say that main difference is insulation or
property of insulation to withstand voltage stress.
| Is This Answer Correct ? | 14 Yes | 3 No |
Post New Answer View All Answers
please send previous exams question papers
Define pole pitch?
What is an 86-P or an 86-A trip
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
Why air circuit breaker off due to power failure?
What are the transformer losses?
What is the restart inhabit setting in ABB spam150c relay (Motor protection relay)
What is the types of HT motor testing
what is invertor supply and raw powersupply
How much ph is maintained of water resistance starter for slipring induction motor ?
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?
Why is the starting current high in dc motor?
1))why we run three phase or three different circuit from a single conduit 2)) why not two circuit of different phase run in same conduit?? and why we run same three cicuit of same phae run in single conduit??
I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA
what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing