I have calculated load for an office building which is 1200
KW
as all the load is single phase therefore its 1200 kw single
phase. Now i have to design Transformer and Generator for
this load Please kindly give me exact answer that how much
capacity of Three Phase Transformer and Three Phase
Generator is required for this load.
Answers were Sorted based on User's Feedback
Answer / mayadhar81
1200 kw = 1200*1000 watt
that means 1200000 watt ok
In single Phase for example 1000 watt load,supply 230
volts,current is watts/volts
answer is 1000/230=4.34 amps ok
in 1200000 watts =4.34*1200=5208 amps ok
Per phase current=5208/3=1736 amp
three phase transformer/ generator=1736/1.392=1247 kva dg
or transformer is used for full load.
Then you have used 1500 kva dg or transformer
and put it 80% load.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / niraj
Answer #1 does not take into account the power factor.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahendra
KVA=KW/cosφ
KVA= 1200/.9
KVA=1333KVA @80%
KVA= 1500KVA
Is This Answer Correct ? | 0 Yes | 0 No |
what should be the spaciing between street lights designed for a manufacturing location. any IS codes?
How to convert from HP to BHP please explain????????
33kv Rated output avilable in market (any where in india)
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
what is the concept of directional power?
Why Phase to Neutral get spark
why corona ring is used in out door switchyard lightning arrestor
why our power production in multiples of 11.
HOW DOES THE PERCENTAGE DIFFERENTIAL PROTECTION WORK IN POWER TRANSFORMER
I have a 380 KVA DG set. How can i find out 1. My Fuel Consumption per hr ? 2. Electricity produced in 1 Hr. ? 3. If load varies then how does it affect fuel consumption & electricity produced ? Please HELP !!! Really need an answer.
what happen if generator exitation lost?
what is 11kv cable