I have calculated load for an office building which is 1200
KW
as all the load is single phase therefore its 1200 kw single
phase. Now i have to design Transformer and Generator for
this load Please kindly give me exact answer that how much
capacity of Three Phase Transformer and Three Phase
Generator is required for this load.
Answers were Sorted based on User's Feedback
Answer / mayadhar81
1200 kw = 1200*1000 watt
that means 1200000 watt ok
In single Phase for example 1000 watt load,supply 230
volts,current is watts/volts
answer is 1000/230=4.34 amps ok
in 1200000 watts =4.34*1200=5208 amps ok
Per phase current=5208/3=1736 amp
three phase transformer/ generator=1736/1.392=1247 kva dg
or transformer is used for full load.
Then you have used 1500 kva dg or transformer
and put it 80% load.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / niraj
Answer #1 does not take into account the power factor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahendra
KVA=KW/cosφ
KVA= 1200/.9
KVA=1333KVA @80%
KVA= 1500KVA
| Is This Answer Correct ? | 0 Yes | 0 No |
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
What is the gain of 1-s/1=s at 1 rad/sec?
Where can I get CPWD electrical shedule rates in web? please help me.
we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz
why transformer is rated in KVA ?
Cb closed condition if there is a tcs fail whether cb will trip or not
the inertia constants of two machines are respectively 30and 42 MJ per MVA.when the change in frequency due to change in load in first machine is 12 Hz,the change in second machine frequency will be?
The temperature rise in the sys, which leads to ….. a) Increases stress& length b) increases stress but decreases length c) Decreases stress & increase length d) decrease stress & length
1 Answers Engineers India Limited,
what deffrence between KW $ KVA ?
what is the difference in inductance and resistance.both oppose the flow of current but how.resistance having + ve power in both cycle while inductance having both power.
my field of interest is T&D. plz tell something about that.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)