1KVA transformer of different frequencies of
50hz,100hz,500hz&1000hz. which one of these transformer has
big size? Give reason
Answers were Sorted based on User's Feedback
Answer / gajendra singh
50Hz transformer has large size as for the fixed kva but as the frequency increase and kva fixed than size of x-mer decrease.
because of B-H loop magenetation characteristic
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amrit
He is talking about same KVA t/f.
we r not changing anything but the size... how?
keeping voltage per turn as same in both cases..
we decrease the flux in same proportion as the freq.
increased to keep freq.*flux = const.
now flux decreased reduce the area of the core to keep flux
density same.
Hence size of t/f will b small with high freq.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / hardik (tata chemicals ltd)
As above V/f= flux
1) in case of increase fqr flux is inversely praposnal to
friqunce (vtg = constant) so flux will be reduce so related
to core losses also decrease size of core also we can
decrease..but in this case as per emf equation vtg is also
praposnal to flux so we have to increase wdg turns so size
of all bulk of X'mer become big ,in short it is true size
is inverse praposnal to frequnce but we can not get much
different b'wen as above X.mers
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lucky
size is inversily proportional to frequency...
so 50hz transformer will be larger in size
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / er. ankush miglani 9718151073
Mr. Mohh. Shahid
if v/f=flux
then fr is inversly proportional toflux
then if u increase the fr the flux will decrease
and so the core area also decreases.
all this is for the constant voltage
but for the constant flux the fr is directly proportional
to the voltage
so if the voltage increases the insulation increases and
hence the size of the transformer increases.
then in both the casesthe action is opposite
then how can u say that the size of the transformer
increases.
check it out
| Is This Answer Correct ? | 1 Yes | 6 No |
Answer / mohd shahid
See V/F= flux
Now Case I : Voltage is constant
if we increase the frequency thn flux will increase which
ultimately increases the hysteriss loss so in order to
dessipate the loss we hav to increase the transformer size.
NOW Case II: Flux is constant
In this case also size of transformer will increase with
increase in frequency bcoz voltage will increase in order
to maintain the constant flux. Hence more insulation will
be reqd so size ultimately increases.
| Is This Answer Correct ? | 3 Yes | 30 No |
on which power factor synchronous motor run
HOW TO CALCULATE S/C,O/C,E/F OF ACB.
What is ferro-resonance in electrical system? Why it occurs and what are measures to prevent it?
how to find diesel consumption of 600kva DG per hours????
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
what is difference between ac1 and ac3 contactor and why it is needed to be selected?
how much GROUND & NEUTRAL VOLT maintain in data center.
Which motor has more efficiency ;Synchoronous or Induction motor ?
in power generator normaly voltagr betwween esth to neutral is 0 but my work place generator show the volatge is 60v any body know why? thanks
Why negative feedback is preferred in the control system?
what is phase voltage phase current line current and their usage? provide diagram
ELECTRICAL MACHINE
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)