How to take Transformer oil Break down voltage test?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 119 Yes | 10 No |
Answer / sri rama murthy
the breakdown voltage need not be 50kv but the min BDV is
30kv at 2.5mm gap between the electrodes
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / hamed
Regarding the withstand voltage I think It depends on the
type and quality of the oil itself.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / deepak sharma
Please anyone can tell me the dia. of the electrodes?????
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / v.b.vijay anand
At first thing you maintain the electrical norms..To Take one sample from top of Transformer and one from the
bottom of transformer.
On before take oil samples you should confirm the moisture particles removed are not..
And then removed the air boubles in that vessel between the electrode...
The BDV of oil should withstood min 50 KV...
The gap between the test sample is 2.5mm maintained..
Voltage should be gradually increased from 0.
You will wait min 30min then only you will get good result..
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad owais
tell me why take sample both side (top/bottom)?
why not take from bottom any problem
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saravanan.m
*Take one sample from top of Transformer and one from the
bottom of transformer.
*The BDV of oil should withstood min 50 KV
*The gap between the test sample is 2.5mm maintained
*Each sample(top/bottom) should be checked seperately
*Procedure
a.Voltage should be gradually increased from 0.
b.At one point Flash will take place and that point is
termed as Bread down Voltage.
*If its withstand means the viscosity of transformer oil is
good
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / suthagar.s
that means the transformer oil withstand the temparature
capacity that is called as breakdown voltage test in
transformer
| Is This Answer Correct ? | 6 Yes | 45 No |
Amoung all classes of electric machines, why the transformer uses oil as one medium of cooling?
where connected OLTC for transformers?
what is the relevance of knee point voltage in protection and metering grade CT ? and basically what is knee point voltage ?
What are the tests carried out on transformer while testing at sites?..Pls explain me in detail
how dg's working of 1000kva.
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
how the phase convertor changes the no. of phases
Why do we use only Sinusoidal Wave in AC supply why not the Square,Triangle or Sawtooth etc?
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
how to convert the KVAR to microfarad??????????????????
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
Difference between rating factor of cable and derating factor of cable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)