How to take Transformer oil Break down voltage test?

Answers were Sorted based on User's Feedback



How to take Transformer oil Break down voltage test?..

Answer / dinesh kumar

TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage

Is This Answer Correct ?    119 Yes 10 No

How to take Transformer oil Break down voltage test?..

Answer / selvan

answer 1 is very correct.

Is This Answer Correct ?    34 Yes 7 No

How to take Transformer oil Break down voltage test?..

Answer / sri rama murthy

the breakdown voltage need not be 50kv but the min BDV is
30kv at 2.5mm gap between the electrodes

Is This Answer Correct ?    26 Yes 3 No

How to take Transformer oil Break down voltage test?..

Answer / hamed

Regarding the withstand voltage I think It depends on the
type and quality of the oil itself.

Is This Answer Correct ?    3 Yes 1 No

How to take Transformer oil Break down voltage test?..

Answer / deepak sharma

Please anyone can tell me the dia. of the electrodes?????

Is This Answer Correct ?    1 Yes 0 No

How to take Transformer oil Break down voltage test?..

Answer / v.b.vijay anand

At first thing you maintain the electrical norms..To Take one sample from top of Transformer and one from the
bottom of transformer.
On before take oil samples you should confirm the moisture particles removed are not..
And then removed the air boubles in that vessel between the electrode...
The BDV of oil should withstood min 50 KV...
The gap between the test sample is 2.5mm maintained..
Voltage should be gradually increased from 0.
You will wait min 30min then only you will get good result..

Is This Answer Correct ?    0 Yes 0 No

How to take Transformer oil Break down voltage test?..

Answer / muhammad owais

tell me why take sample both side (top/bottom)?
why not take from bottom any problem

Is This Answer Correct ?    0 Yes 1 No

How to take Transformer oil Break down voltage test?..

Answer / saravanan.m

*Take one sample from top of Transformer and one from the
bottom of transformer.
*The BDV of oil should withstood min 50 KV
*The gap between the test sample is 2.5mm maintained
*Each sample(top/bottom) should be checked seperately
*Procedure
a.Voltage should be gradually increased from 0.
b.At one point Flash will take place and that point is
termed as Bread down Voltage.
*If its withstand means the viscosity of transformer oil is
good

Is This Answer Correct ?    4 Yes 7 No

How to take Transformer oil Break down voltage test?..

Answer / suthagar.s

that means the transformer oil withstand the temparature
capacity that is called as breakdown voltage test in
transformer

Is This Answer Correct ?    6 Yes 45 No

Post New Answer

More Electrical Engineering Interview Questions

what is difference between 5A and 100A CT constructional wise and operation?

1 Answers  


what is the power ratio between power in star and delta circuit?

3 Answers  


At what condition differential relay will act in transformer and ht motor?

1 Answers   Equate,


why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?.

10 Answers  


whatis the commertial spec. of distribution boards ?

0 Answers   Bosch,






Why a dc generator gives result during two different condition,- 1)separately exited gen.- Eg=110 V, field current=0.25 A. 2) self exited gen.- Eg=30 V, field current=0.025 A.

1 Answers  


Why is transformer a machine

1 Answers   Grasim,


what are the highly demanded courses for electrical engg. who finished his b.tech

2 Answers  


what are symmetrical and non symmetrical components in electrical installation.

0 Answers  


why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?

0 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd,


what is power factor

3 Answers  


when transformer in load condition neutral earth testing wheater we can do it or not

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)