How to take Transformer oil Break down voltage test?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
Is This Answer Correct ? | 119 Yes | 10 No |
Answer / sri rama murthy
the breakdown voltage need not be 50kv but the min BDV is
30kv at 2.5mm gap between the electrodes
Is This Answer Correct ? | 26 Yes | 3 No |
Answer / hamed
Regarding the withstand voltage I think It depends on the
type and quality of the oil itself.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / deepak sharma
Please anyone can tell me the dia. of the electrodes?????
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / v.b.vijay anand
At first thing you maintain the electrical norms..To Take one sample from top of Transformer and one from the
bottom of transformer.
On before take oil samples you should confirm the moisture particles removed are not..
And then removed the air boubles in that vessel between the electrode...
The BDV of oil should withstood min 50 KV...
The gap between the test sample is 2.5mm maintained..
Voltage should be gradually increased from 0.
You will wait min 30min then only you will get good result..
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad owais
tell me why take sample both side (top/bottom)?
why not take from bottom any problem
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saravanan.m
*Take one sample from top of Transformer and one from the
bottom of transformer.
*The BDV of oil should withstood min 50 KV
*The gap between the test sample is 2.5mm maintained
*Each sample(top/bottom) should be checked seperately
*Procedure
a.Voltage should be gradually increased from 0.
b.At one point Flash will take place and that point is
termed as Bread down Voltage.
*If its withstand means the viscosity of transformer oil is
good
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / suthagar.s
that means the transformer oil withstand the temparature
capacity that is called as breakdown voltage test in
transformer
Is This Answer Correct ? | 6 Yes | 45 No |
what is difference between 5A and 100A CT constructional wise and operation?
what is the power ratio between power in star and delta circuit?
At what condition differential relay will act in transformer and ht motor?
why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?.
whatis the commertial spec. of distribution boards ?
Why a dc generator gives result during two different condition,- 1)separately exited gen.- Eg=110 V, field current=0.25 A. 2) self exited gen.- Eg=30 V, field current=0.025 A.
Why is transformer a machine
what are the highly demanded courses for electrical engg. who finished his b.tech
what are symmetrical and non symmetrical components in electrical installation.
why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
what is power factor
when transformer in load condition neutral earth testing wheater we can do it or not