What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answers were Sorted based on User's Feedback
Answer / electrical in detail
(1) Core Balance or Magnetic Balance of a transformer is well needed. This test is carried out to determine inter turn faults or magnetic imbalance in transformer.
(2) It is very well known that each turn of the winding of a transformer is isolated from other turn through appropriate insulation. A properly designed transformer of 11 KV / 415 V means applying 11 KV on one side will produce 415 V on other side and vice versa. Now if insulation between turns of a winding loses their property, then turns of the winding are short circuited and this situation is called inter-turn fault.
(3) When an inter-turn fault occurs, magnetic property of transformer is imbalanced and this imbalance is conveyed to secondary side of the transformer as the two windings are connected magnetically. It means voltage that is produced by mutual induction will also get affected. To identify this imbalance, magnetic or core balance (in fact, imbalance) test is carried out.
(4) This test is generally performed on STAR side of the transformer. Forgetting the international nomenclature, let us name three leads of STAR side as R1, Y1 and B1 while that of other winding as R2, Y2 and B2.
B1 is kept opened. A supply of say 440 V is applied between R1 and B1. Next step is to measure various voltages between different phases:
V (R1-Y1) = V (R1-B1) + V(Y1-B1)
For example,
440 V = 250 V + 190 V
(5) As both the windings are connected magnetically, applying voltage to star winding will induce voltage on other winding. Induced voltage in other winding shall be in same proportion to applied voltage at star side. But if, any inter turn shorting is there, the voltage induced on the secondary winding will not be in proportion to the applied voltage.
This is an indicative test only. Accurate results can be obtained in conjunction with other tests.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / joshi nikhilesh
appliade volage IN H.V SIDE APPLIADE VOLTAGE IN L.V SIDE
RY rn
measured voltage measured voltage
RY,YB,BR rn,yn,bn rn,yn,bn
and reapit this all step appliade YB,BR yn,bn and
measured abouve step
| Is This Answer Correct ? | 0 Yes | 0 No |
This is kiran kishore from IEMCO MUSCAT
Can any one explain why this magnetic balance test performed
on star side only? is there alternative methods for this
test? in my knowledge 1. phase in method
2. phase out method.
give me the clear idea. can u explain if tertiary winding
also present then how this test going to be performed?
i hope you guys will give me clear explanation to all my
quires.
THANKS®ARDS
K KIRAN KISHORE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jac
Additional Question Regarding This Issue, What if i supply
on Primary side H1-H2 of Single phase (220/0V)(L1=220V
L2=0V)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sreekanth p singh
i just want to know wether this test shall be carried out on
a built core with designed no. of turns of L.V windings only
wound on it.....
please help nyone..
i'm just a student in dis field
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / manoj
all answers are good but i want to know what interpretation do u make by the results?
| Is This Answer Correct ? | 1 Yes | 7 No |
Answer / ketan
i am ketan more (be electrical)
magnetic balance test
1) step1 given 400v R&Y PHASE ONLY. THAT TIME B PHASE OPEN
OR NOT CONNECTED SUPPLY
MEASURE VOLTAGE RY & YB & BR
READING IS RY=400V (GIVEN VOLTAGE)
YB= (3/4 RY) VOLTAGE
BR= (1/4 RY) VOLTAGE
THISE READING COME MEANS TRANSFORMER IS OK OR MAGNETIC
BALANCE OF PHASE IS OK
| Is This Answer Correct ? | 6 Yes | 12 No |
Answer / j.kesavan
austin hai, iam working in field ,any thing problem in
tr ,we are check py side tr give low voltage two phasecheck
sy is good no problem ,py any thing thing short breaker
will trip.py is good we will get sy voltage is good ratio.
| Is This Answer Correct ? | 5 Yes | 26 No |
What is Lockout Relay and what is use of it in electrical installation
IN 1000kva transformer where the oil and winding temperature sensors is connected
As per IS why should the control be taken only from R phase, why not from B or Y phase??!!
hello... i am preparing for GET. please send me previous papers..
why we connect dg neutral with ground?
how is working d.c amps meter?how to connect the dc ammeter inthe circuite?
my company total load is 1000kw, 415volt, all load are inductive load. incoming powerfactor is .8. we want to have0.95 pf connecting capacitors. so now how much rating of capacitors we have to connect? show how?
LT cable fault chaecking equipment and to find out the distance at what distence it failure . Name and where it is available?
0 Answers Himatsingka Seide Ltd,
How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.
why power factor is lagging and leading(i.e -1to +1)
what is the role of transistor in Circuit?
why do the alternator doesnt have open circuited windings in armature???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)