How can we measure the frequency of a rotor running in full
load condition? Explain the method of measuring.
Answers were Sorted based on User's Feedback
Answer / nanda
U can first measure the rotor speed at full load using a
tachometer..note down the Rated speed frm the panel board
and take it as NS.. rotor speed as NR.
Slip is equal to NS-NR/Ns....so the rotor freq Fr is
slip * AC supply frequency
Is This Answer Correct ? | 22 Yes | 1 No |
Answer / manikiran
Frequency of a rotating machine can be found by Stroboscope..
It makes use of Stroboscopic Effect.When the frequency of
the Incident light is equal to the rotating speed (measured
as frequency of the point moving ) it appears to be
static...and the corresponding speed gives the speed of the
machine..
Or it can also be measured by a tachogenrator...
Is This Answer Correct ? | 8 Yes | 3 No |
transformer spections :: input voltage 0-110-230v; output volage 0-10-12-14v; amp=3A using CRNO CORE, capcaity=50VA primary turns = ? ; secondry turns =?
Why is reating of t/f in kva but for inverter in kw ?
What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
why we r using 4-20ma instead of 0-20ma in instrumentation
How many types of faults are there in 3 phase power system?
Is it possible to convert Dependent sources to its equivelent current or voltage Sources ?????
why there is a phase shift lies between primary and secondary voltages of a transformer?
Why syn. Generators are used for the production of electricity?
Which of the following can be operated at higher frequencies ? -SCR -MOSFET -IGBT
We have got the HT connection of 1000 KVA in which we have installed a seprate APFC panel at the PCC end & seprate KWH meter is installed. My question is that does the KWH reading shown in the meter is a part of the Consumption ???? ( approx 500 units is shown)
1) Why distributiion system decided 11 kv, 33 kv, 66 kv, 132 kv, 220 kv, 400 kv, 2) In 3 Phase line terminal of capacitor, why used for power factor improvement. 3) Why used rating KVA in transformer?