What is the maximun current carring capacity in per phase
for three pole 100anps rating ncb
Answers were Sorted based on User's Feedback
Answer / smartboy123
current capacity of mcb is marked on 3pole mcb is 100amps
then each pole is design to carry 100 amps it means per
phase 100 amps
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / shri..
Actually the MCBs are tested 120 % load.
We can put the load up to 100% means 100 amps per phase.
| Is This Answer Correct ? | 10 Yes | 3 No |
what is the potential of 11kv A.B.Switch
different between circuit breaker & switchgear & relays
how do you test the capacitor bank ?
In D O l starter motor starts as a star connected ,then in star delta starter also motor initially starts as star how come star delta is preferred from dol
which of the following elements is not present in stainless steel
why ct secondary side shortlink provided? its open what will happen?while running ?
sir what is the minimum IR value of 11 KV alternator?
what is need of air gap in expansion section in busbar?
what is mutual induction principle?
Why does a TV set have two pin plug whereas the moniter of a computer has three pin plug? Isn't the earthing protection required for the TV set
what transformer we used normally and upto which kva?
i completed my b.tee(eee) in 2009, but i did not join any job, i joined in my father business, now i want to join any good job, please suggest any course for me
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)