What is STEP VOLTAGE ?
Answers were Sorted based on User's Feedback
Answer / amir
step voltage is the voltage between your legs in
calculation of earthing system.
| Is This Answer Correct ? | 68 Yes | 11 No |
Answer / rod
If a high voltage source strikes the ground the voltage is
disenpated though the ground in widening circles until it
is reduced to zero, if a person was standing near the
centre of the discharge there would be a voltage difference
between 2 points the closer to the discharge point the
higher the voltage, as an example cows have been killed
when they are close to a lightning strike but not hit by
the lightning, this is due to the voltage difference
between their legs, ie step voltage
| Is This Answer Correct ? | 54 Yes | 3 No |
Answer / trevor
Think of a perfectly calm lake or pond, not a ripple in it.
Then you throw a large rock out into it. Ripples start from
that point and disperse 360 degrees outwards. The ripples
near the centre are higher and closer together than the
ripples further away from the point of impact, eventually
decreasing to no ripples at all as the surface tension of
the water takes over.
Now, in place of a lake or pond you have a field with a
high voltage(tension) power line in it; let's say 13,800
volts.
In place of the rock you have one of the high voltage lines
from the power pole that dropped into the field and is
making contact with the ground.
As the energy leaves the line and enters the ground, it
disperses outwards 360 degrees, gradually being absorbed by
the earth (or meeting enough resistance from the earth to
negate the energy) Unlike a pond, however, the energy
doesn't disperse evenly as different types of soil provide
less or more resistance than others.
As in the pond, the voltage that is nearer the point of
impact is higher than the voltage further out, i.e., 13,800
volts at impact, 9,000 volts a metre away, 6,000 volts a
metre from that and so on.
The concern is this; if you started walking towards the
downed line (at around one metre per step) from let's say a
hundred metres away, at first you'd be walking on ground
that has no voltage present. As you got closer the voltage
between your forward leg and back leg would be 100 volts.
Next step, 400 volts, then 1,000 volts. At some point
closer to the centre, you would take a step that is of a
high enough voltage (difference in potential between your
front and back foot) to either go through the footwear you
have on or jump over your footwear and go directly into
your legs. You are then creating a pathway for the voltage
to travel in and would have all of that voltage and
ampacity go through you.
| Is This Answer Correct ? | 35 Yes | 2 No |
Answer / hajhooj
when hv strikes ground it creat a voltage on the ground
mass around the point of the strike.this voltage is fading
as the point goes further from the point of strike.voltage
level at equal distance from the the center is equal.now
the step voltage is the difference in voltage between two
point which are located one meter apart from each other on
one line that is coming from the point of strike.
| Is This Answer Correct ? | 27 Yes | 1 No |
Answer / k.prakashchandra
If a phase wire falls on the ground ,if you stand almost on
the line between the neutral grounding point and fault point
you receive the maximum step voltage, if your are feet are
apart along this line.The intensity increases if the fault
is at a short distance from the neutral grounding and you
get a heavy jolt depending on the phase voltage.The step
voltage is equal to phase voltage x distance between your
feet / the distance between fault and neutral ground.
Luckily ,line trips almost instantly.
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / abdul
correct term is "Step potential"
It is voltage formed between legs when walking in a high
voltage area ie a substation. we have to make small steps
while walking in such substation yard. Lambs and small cows
usually kills when thy jumb.
Another term is "Touch potential"
This is also dangeorous. to reduse the risk, all substation
yards filled with stone metals.
| Is This Answer Correct ? | 4 Yes | 11 No |
Answer / benji
It is the voltage waveform that occurs when a switch is
turned on.
| Is This Answer Correct ? | 17 Yes | 71 No |
how to calculate power loss cost of aluminium conductor and copper conductor?500v,100A,68mm area squre busbar.
what the purpose of data retrivala panel in substation
what is dc voltage?
i have 6oo kva dry type transformer and its neutral is not grounded even body of transformer ground i want to know it is safe or not ?
what r the preventive maintenance of air compressor
what will happen if any motor runs long time with star connection in400vA.C. system
How much difference can there be between HT & LT KWH unit consumption at the same load?
what is deffrent alternatid and gernater
when we supply in primary side of transformer then the supply goes in secondary side?how it works?
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
How many types of DC current
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)