Why generating power limited to 11kv?
Answers were Sorted based on User's Feedback
Answer / 7anoter4
There are generators of which supply voltage is up to 30 kV
[usually 22-23 kV for 500-800 MVA].The problem is the
insulation- will be very expensive for higher voltage-the
generator it self and the auxiliary switchgear and
transformer. A medium voltage generator and a step-up
transformer is cheaper and more convenient for maintaining.
| Is This Answer Correct ? | 17 Yes | 4 No |
Answer / rahul anand
The generating
capacity of
power plant is
given by
multiple of form
factor(1.11)
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / abdul muneeb khan
ABB research
http://www.abb.com/cawp/seitp202/c1256c290031524bc12567310024e1e4.aspx
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / chyray
that are no limit on generating "Voltage"
e.g. Singapore HT network system are 22Kv, so standby
Generator are 22kv or 415v at LT side.
BTW generating power unit are "KVA" or "MVA" not voltage.
| Is This Answer Correct ? | 0 Yes | 6 No |
What happened to installed high capacity conductor for smaller current rating?
Define corner frequency?
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
1kva=how many kw & amps
Why indicated only R.Y.B to phase.
why they charge more bill for low power factor rather than high power factor
What is the real use of reactive power in a electrical system other than loss (inductive &capacitive).I want to know its real physical significance.
Dear friends, i would like to know that what is the exact function of 'exciter winding' & 'aux winding' in Alternator?
in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel
electrical engineering giving priority for insulators rather than conductors, why ?
What makes the difference between 50Hz supply and 60Hz supply which one is economical? What is the use of using increased frequency?
15hp motor wound by 0.9mm & 0.95mm magnet wire. at no load test it draw 4.2A current. Another motor with same condition draw 9.2A current. How can that occur? pls help
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)