Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much loading in terms of ampere can put on 5 MVA,33/11
KV TRANSFORMER having rated current 263 Amp ?????????

Answers were Sorted based on User's Feedback



how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / sunil bhuarya

its sunil bhuarya
ans of this question is ut self in the que.
how-
5000/(root3)*11=262.43 aproxx=263
and in case of overloading it becomes 300 to 315A.

Is This Answer Correct ?    38 Yes 7 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / ynrao

263 Amps as the question itself says

Is This Answer Correct ?    29 Yes 7 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / serwox

Answer depends on what percentage overload a transformer can
accept. For a tx that can accept a 120% overload, the
current is 315A.

Is This Answer Correct ?    20 Yes 5 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / pravin

Actually it depends upon designer. If we asked designer to
designed for 125% overload, he will provide cooling per
current loading on 125% overload to restrict Hot Spot Temp.
of the winding & Top oil temp. respective to max. ambient
temp.
In this case, we can provide loading of 437A in
terms of ampere on top rating with Hot spot temp & top oil
temp in control on top rating. Actually transformer has
three rating OA/FA/FA. If this transformer is OA/FA/FA then
we can provide this loading.
If it is self cooled then 263A is max. loading.

Is This Answer Correct ?    5 Yes 1 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / sunil kumar das

above answer is also correct.we can put less than full
load current.

Is This Answer Correct ?    6 Yes 3 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / jayant subhash golait

If the word rated current comes,then it is actually safe n maximum permissible limit....Obviously,the machine will misbehave when crossed this limit...to save the machine or to avoid failures,extra cooling may be required that is also within tolerable range...again the manufacturer may declare that value as a rated current which is itself little bit away from tripping or breakdown or danger zone of tolerance....finally ,it is solely depend upon manufacturer n in turn the quality of raw material used to design the machine....

Is This Answer Correct ?    1 Yes 0 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / narayanan surendran

The question did not talk about cooling and Tap Changer Type.
If over loaded, voltage drop and over heating may occur.
Therefore given rated current 263 A is correct.

Is This Answer Correct ?    0 Yes 0 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / sam

That depends on the rated output's power factor and the
load power factor.

Is This Answer Correct ?    2 Yes 3 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / har

300amp

Is This Answer Correct ?    8 Yes 10 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / pankaj

Normayy transformer gives max efficieny at 75% of its rated
capacity because in that case cu loss = iron loss.

Is This Answer Correct ?    1 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

can anybody find out the result. I am lil bit confused about my equation.

1 Answers   Student,


WTA used cb?

0 Answers   Tagros,


What happens if the capacitive reactance of a transmission line is very high?

5 Answers   ABB, Power Grid,


what is the tolerance for the magnetic balance test conducted on the distribution transformer?

0 Answers  


What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.

2 Answers  


what do you mean by power factor ? in new view

3 Answers   BDL,


what is the difference in between short time and continuous rating?

1 Answers  


what is the effect of power factor on DG supply,i mean to say what will the effect if we add capactors on dg supply.

4 Answers   HCL,


How to calculate the rating of ELCB OR RCCB for an equipment?

2 Answers  


If u have 60KVA UPS, than tell me how systems ( computers ) u may connect?

3 Answers   Thomson Reuters,


what determins the amount of voltage produced by a voltaic cell?

1 Answers  


What are the different types of LT Cables?

0 Answers   Nabard,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)