how much loading in terms of ampere can put on 5 MVA,33/11
KV TRANSFORMER having rated current 263 Amp ?????????
Answers were Sorted based on User's Feedback
Answer / sunil bhuarya
its sunil bhuarya
ans of this question is ut self in the que.
how-
5000/(root3)*11=262.43 aproxx=263
and in case of overloading it becomes 300 to 315A.
| Is This Answer Correct ? | 38 Yes | 7 No |
Answer / serwox
Answer depends on what percentage overload a transformer can
accept. For a tx that can accept a 120% overload, the
current is 315A.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / pravin
Actually it depends upon designer. If we asked designer to
designed for 125% overload, he will provide cooling per
current loading on 125% overload to restrict Hot Spot Temp.
of the winding & Top oil temp. respective to max. ambient
temp.
In this case, we can provide loading of 437A in
terms of ampere on top rating with Hot spot temp & top oil
temp in control on top rating. Actually transformer has
three rating OA/FA/FA. If this transformer is OA/FA/FA then
we can provide this loading.
If it is self cooled then 263A is max. loading.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sunil kumar das
above answer is also correct.we can put less than full
load current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / jayant subhash golait
If the word rated current comes,then it is actually safe n maximum permissible limit....Obviously,the machine will misbehave when crossed this limit...to save the machine or to avoid failures,extra cooling may be required that is also within tolerable range...again the manufacturer may declare that value as a rated current which is itself little bit away from tripping or breakdown or danger zone of tolerance....finally ,it is solely depend upon manufacturer n in turn the quality of raw material used to design the machine....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / narayanan surendran
The question did not talk about cooling and Tap Changer Type.
If over loaded, voltage drop and over heating may occur.
Therefore given rated current 263 A is correct.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sam
That depends on the rated output's power factor and the
load power factor.
| Is This Answer Correct ? | 2 Yes | 3 No |
can anybody find out the result. I am lil bit confused about my equation.
WTA used cb?
What happens if the capacitive reactance of a transmission line is very high?
what is the tolerance for the magnetic balance test conducted on the distribution transformer?
What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.
what do you mean by power factor ? in new view
what is the difference in between short time and continuous rating?
what is the effect of power factor on DG supply,i mean to say what will the effect if we add capactors on dg supply.
How to calculate the rating of ELCB OR RCCB for an equipment?
If u have 60KVA UPS, than tell me how systems ( computers ) u may connect?
what determins the amount of voltage produced by a voltaic cell?
What are the different types of LT Cables?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)