how much loading in terms of ampere can put on 5 MVA,33/11
KV TRANSFORMER having rated current 263 Amp ?????????
Answers were Sorted based on User's Feedback
Answer / sunil bhuarya
its sunil bhuarya
ans of this question is ut self in the que.
how-
5000/(root3)*11=262.43 aproxx=263
and in case of overloading it becomes 300 to 315A.
| Is This Answer Correct ? | 38 Yes | 7 No |
Answer / serwox
Answer depends on what percentage overload a transformer can
accept. For a tx that can accept a 120% overload, the
current is 315A.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / pravin
Actually it depends upon designer. If we asked designer to
designed for 125% overload, he will provide cooling per
current loading on 125% overload to restrict Hot Spot Temp.
of the winding & Top oil temp. respective to max. ambient
temp.
In this case, we can provide loading of 437A in
terms of ampere on top rating with Hot spot temp & top oil
temp in control on top rating. Actually transformer has
three rating OA/FA/FA. If this transformer is OA/FA/FA then
we can provide this loading.
If it is self cooled then 263A is max. loading.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sunil kumar das
above answer is also correct.we can put less than full
load current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / jayant subhash golait
If the word rated current comes,then it is actually safe n maximum permissible limit....Obviously,the machine will misbehave when crossed this limit...to save the machine or to avoid failures,extra cooling may be required that is also within tolerable range...again the manufacturer may declare that value as a rated current which is itself little bit away from tripping or breakdown or danger zone of tolerance....finally ,it is solely depend upon manufacturer n in turn the quality of raw material used to design the machine....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / narayanan surendran
The question did not talk about cooling and Tap Changer Type.
If over loaded, voltage drop and over heating may occur.
Therefore given rated current 263 A is correct.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sam
That depends on the rated output's power factor and the
load power factor.
| Is This Answer Correct ? | 2 Yes | 3 No |
plz tell me about BACK emf and how it generates?
How the oil level of the Buchholz Relay come down.
whether the generating voltage can be made to be transmitted by means of signals to the recieved end or at the consumers end?
why the pressure coil is not present in the three phase wattmeter?
comparision between ACB and VCB
How the over load setting for HT Motors calculated-provided in Numerical Relay
0 Answers Damodar Valley Corporation,
Define resonant frequency?
what is the major difference between dc generator and synchronous generator?
What is evaporator & condencer & compressor
why we permissive overreach in distance protection.where it is applicable to use in long r short lines
For having nonavailablity of 10 Amps fuse, a lineman replace the same with 5Amps two strand, Do he correct ?
3phase lt motor winding how to checking with megger
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)