WHAT IS BASICS TO SELECTION OF 11 kv Trasformer, send any
calculation sheet for selection of transformer
Answers were Sorted based on User's Feedback
Answer / shiva
for any application selection depends on local distribution
(sub station ) transmission ,secondary voltage and finally
depends only on demand KVA of u r plant.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / anuya
Basic & most important factor is transformer capacity which
can be derived by calculating all connected loads at
downstream. It will give the KVA rating.
Primary-secondary voltage ratio & vector group.
Environmental conditions like temp, etc. Application
Indoor/outdoor.
Cooling type requirement will deside the Xmer will be Oil
cooled or dry type unit.
Impedance of the Xmer.
Load type.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / prabhu gnanasekaran
11 KV transformer or anyother transformer the calculation
of the transformer is done only as per the loads connected
in it(Continious load,stand by load and Auxillary load). No
of motors connected to it,KW rating of the mator, Total
line current of all motors.
If it is 11 KV the your primary side of the transformer is
11 KV thats all. Due to this 11 KV the line current
calcultation will change in the factor of system voltage
level in Line current calculation of the motor.
Is This Answer Correct ? | 8 Yes | 16 No |
What is meant by stator?
why we take transformer reading in kva
how to calculate the no load current in transformer?
what is the defination of electrical engineer.
how to calculate transformer turn primary & secondary side 11kv to 420v
What are motor generator sets and explain the different ways the motor generator set can be used ?
What is auto reclose system in Circuit breakers??
When we have earthing mesh or underground earthing network in industrial plants, weather we have NT-S or NT-C-S kind of earthing system, so eventually weather we must use 4 or 5 wire in 400 volt level (For example 3×150+70 mm2 or 5×150 mm2) in this connection I would like to know exactly the paragraph of IEC or IEEE number
Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.
A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.
what is power factor
how technical is calculated in 11kv line and lt line