Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How can you calculate in detail the VA burden of current
transformer used for Restricted earth fault protection?
Please understand that the CT required here is Class PX or
X. Also please show the calculations for knee point vtg,
stabilizing resistor, magnetising current.

Answers were Sorted based on User's Feedback



How can you calculate in detail the VA burden of current transformer used for Restricted earth fau..

Answer / william lobo

Knee Point voltage is nothing but a point at which the CT
saturates. Thats why its always better to design the CTs
which can operate without saturation even at a voltage
appears in the CT during fault condition. Pls find below
the following formula for calculating the Knee point
voltage.

Vk=2If(Rct+2Rl).

where, If is the current refected to the CT secondary
during fault condition,

Rct is the resistance of the CT which can be adopted by
means of a thumb rule considering the CT ratio,

Rl is the lead resistance i.e. sum of the resistance of the
wire connected between the relay & CT and Impedance offered
by the internal circuitary of the relay

For PS class CT's designed considering the above,burden is
not applicable.

Is This Answer Correct ?    7 Yes 0 No

How can you calculate in detail the VA burden of current transformer used for Restricted earth fau..

Answer / williamlobo

Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.

The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.

Is This Answer Correct ?    3 Yes 3 No

How can you calculate in detail the VA burden of current transformer used for Restricted earth fau..

Answer / william lobo

For PX class CTs , the burden is not normally mentioned .
There the CT is defiened based on the CT kneepoint
voltage , magnetising current etc . The burden is mentioned
in class P CTs

In PX class CTs the kneepoint voltage is normally based on
the max fault current and a diamensioning factor based on
system X/R ratio

Is This Answer Correct ?    3 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What shocks us , Current or voltage?

21 Answers  


what is induction motor

2 Answers  


do you have some of interview Questions in power and genrator section in general whith answers

0 Answers  


How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?

0 Answers  


what is the diff between mcb and vcb

3 Answers  


How to know of any cable size if there are not written on cabl?

0 Answers   APGenco, El Seif,


Is a induction motor rotate by back emf ? If not , then how it is rotate ?

1 Answers  


Is a 300w induction motor used in a food processor as powerful as a 1000w DC motor.

0 Answers  


What are the different types of dams?

0 Answers  


explain supply side and demand side energy management with advantages & disadvantages

0 Answers  


why nutral and earthing wire connect with each other in main panel board.

2 Answers  


As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)