How can you calculate in detail the VA burden of current
transformer used for Restricted earth fault protection?
Please understand that the CT required here is Class PX or
X. Also please show the calculations for knee point vtg,
stabilizing resistor, magnetising current.
Answers were Sorted based on User's Feedback
Knee Point voltage is nothing but a point at which the CT
saturates. Thats why its always better to design the CTs
which can operate without saturation even at a voltage
appears in the CT during fault condition. Pls find below
the following formula for calculating the Knee point
voltage.
Vk=2If(Rct+2Rl).
where, If is the current refected to the CT secondary
during fault condition,
Rct is the resistance of the CT which can be adopted by
means of a thumb rule considering the CT ratio,
Rl is the lead resistance i.e. sum of the resistance of the
wire connected between the relay & CT and Impedance offered
by the internal circuitary of the relay
For PS class CT's designed considering the above,burden is
not applicable.
Is This Answer Correct ? | 7 Yes | 0 No |
Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.
The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.
Is This Answer Correct ? | 3 Yes | 3 No |
For PX class CTs , the burden is not normally mentioned .
There the CT is defiened based on the CT kneepoint
voltage , magnetising current etc . The burden is mentioned
in class P CTs
In PX class CTs the kneepoint voltage is normally based on
the max fault current and a diamensioning factor based on
system X/R ratio
Is This Answer Correct ? | 3 Yes | 3 No |
What do you mean by an instrument transformer?
our industries ht line so power fluctation(once drop of power please rectify causes
What is OT in a transformer, specify its function.
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
what is meaning of bus raiser???
what is the cable capacity of any load wise .
Is there any abbrevation for STUB in Stub bus protection
how to calculate cable size with respect kw
what is the effect of leading power factor
3 Answers Aurobindo, R L Steels and Energy,
How to convert from HP to BHP please explain????????
what is the meaning of vcc
what is the principal of star delta starter?